I don't know what the receptacle configuration may have been pre 1996. Generators nowadays have a four wire receptacle. Answering your question about the gen set feeder, I would have to say you can't use the three conductors and a ground rod. Technically a ground rod is necessary for the service and the genset but you really can't depend on ground resistance to establish an equipment ground. A four wire feeder as in "to a sub-panel" yes.
|