High amp device!

Hello, I want to start out by saying I have spent the last two hours cruising this forum and finding answers to my questions and potential questions in the future...this is truly a great resource....especialy for new homeowners like me! Anyway, I am looking at purchasing a large blower/dryer (motorcycle/car dryer) for the garage and the spec sheet says it is 19 amps. By my calculations (and feel free to correct me) that is about 2250 watts, I think I remember reading on this forum that a 20 amp circuit could handle 2400 watts.? My question is: would there have to be a dedicated circuit all of the time for me to run this device? I am not sure but I hink there is only 15 amp circuit breakers on the garage outlets. Even if I upgraded the circuit to 20 amps it would still be at 95% capactiy with this device...or am I missing something? Is it even possible/safe? Thanks for your time in advance.
Reply With Quote
  #2 (permalink)  
Old 02-05-2008, 07:49 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 5,307
Thanks: 0
Thanked 148 Times in 143 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
19 times 120 = 2280 watts. 19 amps on a 20 amp breaker is kinda pushing your luck. I would go to a single pole 30 amp breaker because a motor starting draws about 125% of nameplate amps before it reaches its running amps PLUS you have a resistive load (the heater element) Does your garage have a sub panel or are you looking at running the circuit back to the main panel?
Reply With Quote
  #3 (permalink)  
Old 02-05-2008, 08:06 AM
New Member
 
Join Date: Feb 2008
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
jag33560 is an unknown quantity at this point
No subpanel in the garage so I would be running it from the panel in the basement. I am starting to consider going with the smaller dryer that only draws 9.5 amps....I would like to use this around the house and possibly take it over to a friends house. would not be fully usefull if i was tied to one outlet in the garage...not to mention I would have to make sure that anywhere I went had the power....guess I will go with the smaller version. I guess I could use the 9.5 amp just about anywhere, thanks a lot for the feedback!
Reply With Quote
  #4 (permalink)  
Old 02-05-2008, 08:33 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 5,307
Thanks: 0
Thanked 148 Times in 143 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
9.5 times 120 = 1180 watts. are we talking like an industrial hair dryer or a floor model with a fan, sort of like what they use for drying rugs?
Reply With Quote
  #5 (permalink)  
Old 02-05-2008, 04:21 PM
New Member
 
Join Date: Feb 2008
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
jag33560 is an unknown quantity at this point
It is designed for drying off motorcycles....it blows warm filtered air. they have two models and the 19 amp big daddy would be nice to have but not if it is going to cause a lot of hassel just to run it. Leaning more and more towards the 9.5 amp model. Thanks.
Reply With Quote
  #6 (permalink)  
Old 02-05-2008, 06:42 PM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 191
Thanks: 0
Thanked 4 Times in 4 Posts
Speedy Petey is an unknown quantity at this point
What kind of plug does the 19A model have?
Can you provide a link to it?
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
  #7 (permalink)  
Old 02-05-2008, 10:38 PM
New Member
 
Join Date: Feb 2008
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
jag33560 is an unknown quantity at this point
the specs say it has a "heavy duty 3 prong" just like the 9.5 amp model....I can't post a link yet but if you go to motorcycledryer.com and click on "blaster product specifications" it has the info on all the different models. do appliances that push near 20 amps usually have a different plug? Thanks.
Reply With Quote
  #8 (permalink)  
Old 02-06-2008, 07:37 AM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 191
Thanks: 0
Thanked 4 Times in 4 Posts
Speedy Petey is an unknown quantity at this point
Quote:
Originally Posted by jag33560 View Post
do appliances that push near 20 amps usually have a different plug?
They should but many don't.
My point is, if it has a "standard" 15 or 20 amp plug on the cord you do not need, and CANNOT use a 30A breaker.

That site is a real help...not. "Cord-12 ft. Heavy Duty 3 Conductor". This tells us a lot.
Also they use that B-S Craftsman HP rating garbage. Yeah, 8HP (2x 4hp).

I would call them and ask what plug is on the end of that heavy duty cord, and maybe suggest they include this info in their website.

Don't take my frustration personally. I just get pissed when companies give vague or unrealistic information to mask the REAL details.
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
  #9 (permalink)  
Old 02-06-2008, 09:08 AM
New Member
 
Join Date: Feb 2008
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
jag33560 is an unknown quantity at this point
I don't know much about such things but it seems to me that two 4 HP fans would not produce 8 HP! I contacted the company and they said it was a regular 3 prong plug and that it shouldn't be an issue.... Quote "If your home is relatively new, the amp draw should not be a problem. The few times it has been an issue it was with much older homes. If the unit is the only appliance plugged in, it should be fine." Of course I knew this reply would say something to this effect since it is the company selling the product....guess I will give it a shot and if it doesn't work I will return it for the 9.5 amp model....My concern is if I can't use it on a garage outlet with a 15 amp breaker, I have some on a 20 amp but they are in the kitchen and the bathrooms, it would be a pain to run heavy gauge ext. chord everytime I wanted to use it!!! Also, I am in the process of identifying the curcuits in my home to see what is where but it seems to me, and keep in mind I know next to nothing about electricity, that a 19 amp appliance on a 20 amp breaker would not allow anything else to share it....I imagine my wife turning on a light or the toaster (or whatever may share the curcuit) and trip it while I'm using the blower. Thanks for your response Speedy Petey....and don't worry, I never take anything personally.
Reply With Quote
  #10 (permalink)  
Old 02-06-2008, 01:23 PM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 191
Thanks: 0
Thanked 4 Times in 4 Posts
Speedy Petey is an unknown quantity at this point
I will say, no matter how much the embellish the ratings I doubt you'd be able to run that big one consistently on a 15A circuit.
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 13,774
Threads: 8,130
Posts: 35,164
Top Poster: HayZee518 (5,307)
Welcome to our newest member, ScottieChenevey
» Online Users: 58
0 members and 58 guests
No Members online
Most users ever online was 400, 06-22-2009 at 06:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 09:59 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0