im trying to wire a 220 outlet from my breaker box.the wire i have from the breaker box to the outlet has 4 wires red,black,white,bare. how do i hook this up to the breaker? also the plug on the 220 power tool i have is a 3 prong plug and the outlet has only 2 connections on it plus the ground. how do i hook the 4 wire from the breaker box to the outlet?
|

03-03-2008, 05:46 PM
|
|
New Member
|
|
Join Date: Mar 2008
Posts: 7
|
|
|
The Black and Red should be used to connect the two 110 volt legs from the breaker itself to the plug hot terminals.
In your case you need to connect the bare ground wire to the plugs ground terminal and then to the ground lugs in the breaker panel, be careful not to land it on the neutral lugs in the panel, look for other bare or green wires connected to the same place.
The white wire should be cut back and secured at both ends and covered with tape as it is not used. The white is generally used for the neutral or sometimes another hot leg but in this case it is not generally used based on your description.
Make sure to shut off the power at the main before you do anything.
Use of this information, while generally accurate, is at the users liability.
|

03-17-2008, 04:58 PM
|
|
Apprentice
|
|
Join Date: Apr 2006
Posts: 263
|
|
Quote:
Originally Posted by AmeriServ
connect the bare ground wire to the plugs ground terminal and then to the ground lugs in the breaker panel, be careful not to land it on the neutral lugs in the panel, look for other bare or green wires connected to the same place.
|
I thought ground and neutrals land on the same buss bar in residential?
|

03-17-2008, 06:05 PM
|
 |
Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 129
|
|
Quote:
Originally Posted by DKAudio
I thought ground and neutrals land on the same buss bar in residential?
|
Neutrals and grounds can both land on the NEUTRAL bar in ANY main panel. Resi or commercial.
__________________
No, that's not me in the avatar. I just like the picture.
|

03-17-2008, 06:11 PM
|
 |
Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 129
|
|
|
jzinboyz, what is it you are wiring?
What is the load and what size wire and breaker did you get?
__________________
No, that's not me in the avatar. I just like the picture.
|

03-17-2008, 06:20 PM
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,346
|
|
|
I don't know why people think for a 220 outlet you HAFTA use a three wire plus ground! One) its expensive, Two) there's a third wire you won't use, therefore it is wasted. Know your load capacities and buy the cable you need plus the outlet. 20 amp 220 use twelve two plus ground. 15 amp use fourteen two plus ground. All you need to do is tape a piece of black tape on the neutral (white) and you're all set to go! if the receptacle is a two wire with ground twist lock, use the two wire. three phase is almost always 3 pole four wire, the fourth wire is ground (not neutral)
|

03-17-2008, 07:09 PM
|
|
Apprentice
|
|
Join Date: Apr 2006
Posts: 263
|
|
Quote:
Originally Posted by HayZee518
I don't know why people think for a 220 outlet you HAFTA use a three wire plus ground! One) its expensive, Two) there's a third wire you won't use, therefore it is wasted. Know your load capacities and buy the cable you need plus the outlet. 20 amp 220 use twelve two plus ground. 15 amp use fourteen two plus ground. All you need to do is tape a piece of black tape on the neutral (white) and you're all set to go! if the receptacle is a two wire with ground twist lock, use the two wire. three phase is almost always 3 pole four wire, the fourth wire is ground (not neutral)
|
Right, no neutral on 220, 2 hots and equipment ground.
If you are doing an over or similar neutral is usually needed. Some of the electronics (display pad/keys) operates off 110V.
|

03-17-2008, 09:07 PM
|
 |
Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 129
|
|
|
An oven or dryer is NOT a typically a 240v appliance. They are 120/240v. Big difference.
__________________
No, that's not me in the avatar. I just like the picture.
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
 |
» Forum Navigation |
|
|
» Links |
|
» Online Users: 32 |
| 0 members and 32 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 01:54 AM. |
|
All times are GMT -5. The time now is 10:56 PM.