100 amp service

I'm curious. On a 100amp service how many breakers can I hook up?Can I fill the panel without worrying about overloading it?
Is it based on amperage of each breaker combined?
Is there an equasion for this?
Reply With Quote
  #2 (permalink)  
Old 03-23-2008, 12:40 PM
Speedy Petey's Avatar
Master Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 117
Speedy Petey is on a distinguished road
The combined breaker amperage is a meaningless number. It is not uncommon to see 300-400 amps (or more) worth of breakers in a 100A panel.
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
  #3 (permalink)  
Old 03-23-2008, 04:01 PM
HayZee518's Avatar
Master Journeyman
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,197
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
I have to agree with Speedy about the breakers. for instance, 5- 20 amp breakers are 100 amp but you'll never approach the current rating of the breaker in real life unless you have lots of heating circuits. In the front section of the NEC there are several methods of calculating a service entrance load size. other than architects I know of no contractor that actually uses this calculation.
Reply With Quote
  #4 (permalink)  
Old 03-23-2008, 05:29 PM
Speedy Petey's Avatar
Master Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 117
Speedy Petey is on a distinguished road
I do load calcs when I need to. Usually it is not necessary, experience is enough.

Sometimes if I feel it is close, like between 200A and 320A, and the customer is tight with $$$, I will do an accurate calc.

I would not even consider 100A or 150A on ANY new home or most any service replacement.
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
  #5 (permalink)  
Old 03-23-2008, 09:20 PM
HayZee518's Avatar
Master Journeyman
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,197
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Speedy - I had one dwelling in massachusetts that was sooo big I had to use three sub panels. The main was a 200 amp - two subs were 100 amp and one in the garage was a 60. I did that mostly for economics. The home runs were so far from the main, it worked out using the subs.
Reply With Quote
  #6 (permalink)  
Old 03-23-2008, 10:21 PM
Speedy Petey's Avatar
Master Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 117
Speedy Petey is on a distinguished road
Quote:
Originally Posted by HayZee518 View Post
The home runs were so far from the main, it worked out using the subs.
A perfect reason to use subs.
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Forum Navigation
     > Forum News
     > Illustrations
     > You Gotta Laugh!
     > Catch All
     > Plumbing
     > Electrical
     > Flooring
     > Wall Coverings
     > HVAC
     > Stenciling
     > Appliances
     > Audio & Video
     > Projects
     > Faux Painting
     > Painting
     > Gardening
     > Decks & Fences
     > Outdoor Projects
     > Garage Doors
» Links

» Search

Home Repair Forum
Google   
» Online Users: 40
0 members and 40 guests
No Members online
Most users ever online was 388, 07-01-2007 at 01:54 AM.
Powered by vBadvanced CMPS v2.2.0

All times are GMT -5. The time now is 06:37 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0