Quote:
Originally Posted by spotty
I typicaly run a 12-3 and use two seperate receptacles
|
May I ask why? Both a washer and gas dryer are perfectly fine on a shared 20A circuit.
Quote:
Originally Posted by spotty
At least these two outlets don't have to be GFI or AFCI protected,
|
They absolutely DO need GFI protection IF they are within 6' of a laundry sink.
Tamper-proof ONLY applies to areas who have adopted the 2008 NEC with no amendments for that section.
NOT nearly every place has.