Multiple outlets on switch loop
A couple questions about a switch loop. Is it possible to control multiple outlets via switch loop? And can both outlets also be protected by a single GFCI.
Power
Source _____ A ____ Outlet 1 __________ Outlet 2 _____ B _______ Switch ( Loop )
Can the switch control both outlets?
Can the circuit be protected by a single GFCI.
If so would it would it be placed in the circuit: Point A or Point B.
Thanks
Last edited by B Johnson : 04-29-2008 at 11:17 PM.
|

04-30-2008, 03:32 AM
|
 |
Master Journeyman
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,164
|
|
|
any number of outlets can be switched. the downstream outlets are parallel wired to the switch loop. if this is a dedicated circuit, instead of using individual gfci receptacles I'd opt to use a gfci breaker to feed the whole loop. you can use a standard 120 feed to the switch. its output would go to the first outlet input then any outlets downstream of this would use a standard outlet wired to the parallel output of the first gfci.
|

04-30-2008, 03:49 AM
|
 |
Master Journeyman
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,164
|
|
|
switch loop & gfci
look at this diagram - should answer your question.
|

04-30-2008, 06:48 PM
|
 |
Master Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 117
|
|
|
The ONLY way this can work is with a "3-wire" (12/3, 14/3) between receptacle 1 & 2, BUT there is NO way to GFI protect both receptacles.
OK, actually one way. You would need "4-wire" (12/4, 14/4) between the receptacles, but this gets tricky, and good luck trying to find a place that will cut 4-wire. GFI's are cheap anyway.
Do it with a 3-wire in between the use a GFI receptacle at each location wired to LINE side.
__________________
No, that's not me in the avatar. I just like the picture.
|

05-01-2008, 05:37 AM
|
 |
Master Journeyman
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,164
|
|
|
speedy is he wanting to split wire a receptacle? then I can see the three wire otherwise a two wire will do. take a look at my diagram. the downstream outlets would be protected off #1 gfi
|

05-01-2008, 08:17 AM
|
|
New Member
|
|
Join Date: Jul 2007
Posts: 21
|
|
|
The OP is showing the switch at the end of the run, not at the beginning. Speedy is correct, **/3 cable will be necessary between outlets 1 and 2.
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
 |
» Forum Navigation |
|
|
» Links |
|
» Online Users: 52 |
| 1 members and 51 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 01:54 AM. |
|
All times are GMT -5. The time now is 11:20 PM.