Arc breakers required for garage apartment?

For the same garage job (see water heater post immediately before this post), I believe there needs to be arc breakers if people are going to sleep in the finished out second floor. In the upstairs of the garage (2nd story, 20x30'), the wiring can be divided up into zones, where each zone has its own breaker:

1. open area: recessed lights, ceiling fans, attic light, wall switches
2. open area: receptacles around 2nd floor (20x30' area).
3. kitchenette: microwave receptacle (not GFCI).
4. kitchenette: refridgerator receptacle (not GFCI), garbage disposal switch and receptacle, GFCI backsplash receptacle, lights over kitchenette.
5. bathroom: GFCI receptacle, switch, and light over sink, recessed light over camode.

Given the above zones, which need to be on an arc breaker? People will sleep in the living area, which will essentially be "crashing out" on a TV sofa. There is no bedroom, and no beds are used.

It could be coded as a game room, but someone said if people will sleep their then arc has to be used probably for the receptacles around the open area, and something else (which I forgot).
Reply With Quote
  #2 (permalink)  
Old 07-04-2008, 07:05 PM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 136
My Photos: (0)
Speedy Petey is on a distinguished road
What codes cycle are you under?
Does your area even enforce AFCI requirements?
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
  #3 (permalink)  
Old 07-05-2008, 05:18 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,669
My Photos: (0)
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
the reason they adopted the AFCI in bedrooms is because of picture placement on walls. many installations ran the romex up the stud, stapled. the homeowner put up a picture not knowing where the stud was and pierced the romex with a nail or screw. this created a high resistance area that maybe wouldn't trip a normal breaker but would heat up over time creating a hazard. the AFCI like a GFCI would trip upon this penetration.
Reply With Quote
  #4 (permalink)  
Old 07-05-2008, 10:28 AM
lep lep is offline
New Member
 
Join Date: Aug 2007
Posts: 22
My Photos: (0)
lep is on a distinguished road
ok, zones #1 and #4 have some verticals between several wall switches and lights. The supply cable for Zone #4 for the kitchenette comes directly down a stud (way too far from the service box to run at the knee-high receptacle level) and splits into the various receptacles, and in fact runs all throughout the studs. When you think of it, installation of kitchen cabinets for the kitchenette (on floor below countertop, above for plates, etc.) will involve use of a lot of screws placed in the studs. If a GFCI breaker in the service box is used for this zone, and the system is hot when the cabinets are installed, we will know if anything gets hit with a screw or nail.

Thus, I will plan on using AFCI breakers in the service box for zones 1 and 4, and maybe for the open-area receptacles (zone #2) -- since the receptacle cables run horizontally and may be at risk when the sheetrockers do their work.

thx HayZee.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT -5. The time now is 04:43 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0