1 last Question about breakers
My garage has 6 20 amp breakers in the circuit box. I noticed today that some of the wiring is 14\2, now I know this is not to code. Can I switch my breakers out to 15 amp breakers to bring it up to code? I have 3 outlets and a light on 1, 2 outlets and a light on another, 1 outlet and 2 lights on another, 3 lights on 1, garage door on 1, 2 outlets on the last one.
__________________
Jtfoxman
|

04-27-2009, 04:52 PM
|
|
 |
Contractor
|
|
Join Date: Mar 2006
Location: North Carolina
Posts: 903
Thanks: 0
Thanked 44 Times in 42 Posts
|
|
|
Anything with 14/2 can only have a maximum breaker of 15 amp. 12/2 ...20 amp.
change out the 14 g. wire to 15 amp breakers and your good to go code wise.
Note: 12/2 wire can have a 15 amp breaker as well if that makes it easier,
the breaker can be smaller than the wire but never the other way around.
__________________
|

04-27-2009, 05:50 PM
|
|
Handyman
|
|
Join Date: Jan 2005
Location: Hazleton, PA, USA.
Posts: 136
Thanks: 4
Thanked 1 Time in 1 Post
|
|
Quote:
Originally Posted by pushkins
Anything with 14/2 can only have a maximum breaker of 15 amp. 12/2 ...20 amp.
change out the 14 g. wire to 15 amp breakers and your good to go code wise.
Note: 12/2 wire can have a 15 amp breaker as well if that makes it easier,
the breaker can be smaller than the wire but never the other way around.
|
Not quite sure I follow. You say to change out the 14g wire to 15 amp breakers. What do I do? Change all the wire to 12\2 or just change the breakers?
__________________
Jtfoxman
|

04-27-2009, 07:41 PM
|
|
 |
Contractor
|
|
Join Date: Mar 2006
Location: North Carolina
Posts: 903
Thanks: 0
Thanked 44 Times in 42 Posts
|
|
|
No no no....lol.....sorry for the confusion.....what I was saying is that 14/2 wire can only have a maximum 15 amp breaker on it, so REPLACE the existing 20 amp breakers that are on the 14/2 wire with 15 amp breakers, you don't need to touch the wire at all, just replace the breakers.
__________________
|

04-27-2009, 08:29 PM
|
|
Handyman
|
|
Join Date: Jan 2005
Location: Hazleton, PA, USA.
Posts: 136
Thanks: 4
Thanked 1 Time in 1 Post
|
|
|
I get it now. Thanks for your help, I appreciate it.
__________________
Jtfoxman
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 13,762
Threads: 8,125
Posts: 35,136
Top Poster: HayZee518 (5,306)
|
| Welcome to our newest member, Gumbii_Tx |
» Online Users: 26 |
| 1 members and 25 guests |
| No Members online |
| Most users ever online was 400, 06-22-2009 at 06:11 AM. |
» Links |
|
» Sponsors |
|
|
|
All times are GMT -5. The time now is 04:40 PM.