Home Repair Forum



Reply
 
Thread Tools Display Modes
  #1 (permalink)  
Old 08-31-2009, 10:36 AM
OdieTurbo's Avatar
New Member
 
Join Date: Jun 2009
Location: Endicott, NY
Posts: 5
Thanks: 0
Thanked 0 Times in 0 Posts
OdieTurbo is on a distinguished road
Smile Update Old Outlets to New

Okay, house was built in 1914. Wiring was replaced at some point so now I have 2-wire metal shielded cable throughout the 1st floor (2nd floor was upated to 3-wire).

Many appliances etc need 3 wire outlets. What is the proper (safe) way to do this?

One way is to upgrade the 1st floor wiring, but that is a few months off at least. What should I do in the meantime?

Last owner used 3to2 adaptors.
__________________
A house is not a home without a cat... and a motorcycle in the garage.
Reply With Quote
  #2 (permalink)  
Old 08-31-2009, 05:13 PM
pushkins's Avatar
Contractor
 
Join Date: Mar 2006
Location: North Carolina
Posts: 754
Thanks: 0
Thanked 31 Times in 29 Posts
pushkins will become famous soon enough
Basically your two wire outlets don't have a ground, they have a hot and a neutral (two holes) As you mentioned your going to upgrade in a few months there really is probably little you "have" to do right now, until then you can use the two to three adapters or you could replace the outlets in concern with three hole outlets (hot, neutral and ground) you just won't be able to hook up a ground wire for obvious reasons.
As an even better precaution you could replace the outlets in question with GFCI outlets, even without a ground wire attached they will offer some protection.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote
  #3 (permalink)  
Old 08-31-2009, 06:00 PM
Handyman
 
Join Date: Feb 2008
Location: Evansville, In
Posts: 167
Thanks: 2
Thanked 16 Times in 16 Posts
jnaas2 is an unknown quantity at this point
Send a message via AIM to jnaas2
You cant install a grounded receptacle on a two wire system, the bare wire is a equipment ground and a lot of appliances need that to killl the power in case of a shortcircuit. Code does allow a gfi to be installed instead of the 2 prong plug, because a gfi measures the amount of electricity going out verses what comes back and will kill the power in the case of a ground fault and not kill you
Reply With Quote
  #4 (permalink)  
Old 09-01-2009, 07:15 AM
OdieTurbo's Avatar
New Member
 
Join Date: Jun 2009
Location: Endicott, NY
Posts: 5
Thanks: 0
Thanked 0 Times in 0 Posts
OdieTurbo is on a distinguished road
Thanks guys! I'll stop and get a handful of GFCI outlets to replace the couple I need to.
__________________
A house is not a home without a cat... and a motorcycle in the garage.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,946
Threads: 7,778
Posts: 33,345
Top Poster: HayZee518 (4,977)
Welcome to our newest member, mitchell123
» Online Users: 20
0 members and 20 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 03:37 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0