09-05-2009, 03:01 PM
|
|
New Member
|
|
Join Date: Sep 2009
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
|
|
|
50 Amp RV Service
Want to install 50 AMP 14-50R power outlet to exterior wall in garage. Distance from main panel (in garage) is 45 feet. Have purchased 6/3 wire with ground. My concern is the main panel neutral and ground bar are combined. According to my research and the wiring diagram on outlet, the ground and neutral MUST be located on separate bars. My question is, should I install a subpanel with the separate neutral and ground bars with receptacle wired in downstream? It seems to me this is no different than wiring receptacle directly to main panel with ground and neutral on common bar. Thanks for any help---Don
|

09-05-2009, 06:52 PM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
|
|
|
If you want to install a sub panel then the feeder must have isolated ground and neutral at the sub panel along with two driven ground rods. those ground rods terminate at the cabinet or equipment ground bar. IF this is an outlet then it is treated just like any other outlet. you need a weather proof cover if its exposed to the weather. not sure but I believe because you are at grade level, the feed needs to be a 50 amp 240 volt ground fault breaker. the receptacle you named is a straight blade type.
|

09-05-2009, 07:14 PM
|
|
New Member
|
|
Join Date: Sep 2009
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
|
|
|
It is a weatherproof 50A receptacle installed on a far exterior wall of the garage, not a separate structure. So if I understand correctly, the receptacle box itself is not considered a "sub panel" and it's ground and neutral may be directly wired into main panel on the common bus. A sub panel is not required allowing the separation of ground and neutral bus ? Thanks again
|

09-05-2009, 08:33 PM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
|
|
|
yeah, when you wire the receptacle follow directions on the gfci breaker - I'm assuming this is what you are using. if just the two hots go to the breaker then the bare or green ground and white neutral go on the neutral bus in the main panel.
The receptacle wiring the hots go to the outer two blades, the ground to the L shaped blade and the white to the blade opposite the L shaped blade.
|

09-05-2009, 09:33 PM
|
|
 |
Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 189
Thanks: 0
Thanked 4 Times in 4 Posts
|
|
|
No sub-panel is needed.
The ground and neutral land on the SAME bar in the main panel. This IS normal.
No GFI breaker is required, unless of course you want one. I would not.
__________________
No, that's not me in the avatar. I just like the picture. To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 12,944
Threads: 7,777
Posts: 33,327
Top Poster: HayZee518 (4,977)
|
| Welcome to our newest member, Peabarter |
» Links |
|
» Sponsors |
|
|
|
All times are GMT -5. The time now is 11:19 PM.