notches in joists

My plumber put notches in a about 10 joists for a 2 inche pipe and put them in the middle of the joists. Also at the end of the joists, there are 2.5 inch holes and a gas line going through. Beside the gas line holes are notches again for another pipe that is 2 inches. How much will this weaken my floor. Is it dangerous because the gas line is going through? I would appreciate any thoughts. I know code says that the notches should not be in the middle third span. Are the gas notches to big. By the way my joists are 2 X 8 and span about 12 feet. I want to make sure the floor is safe before drywalling the ceiling.

Thanks for any help.

Reply With Quote
  #2 (permalink)  
Old 01-16-2006, 09:10 PM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,159
LazyPup is on a distinguished road

here is an illustration you can share with your plumber




Reply With Quote
  #3 (permalink)  
Old 01-16-2006, 09:18 PM
qas qas is offline
New Member
 
Join Date: Jan 2006
Location: .
Posts: 12
qas
From you illustration it says that no notches are permitted at bottom if less than 4 inches thick. Many books allow nothces at bottom and most joists are 2 inches thick. Is my situation dangerous. It seems the gas line passes code, what about the notches?
Reply With Quote
  #4 (permalink)  
Old 01-17-2006, 05:26 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,346
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Most joists are dimension lumber 1 1/2 or 1 5/8" thick NOT the full 2 Inches as you state. I'd follow Lazypup's drawings to the TEE.
Reply With Quote
  #5 (permalink)  
Old 01-17-2006, 09:50 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
Your local codes may vary, but most all the following for a 2x8" joist:

For a 2x8 joist the max hole is 2 3/8" and max notch is 1 1/4" in outer 1/3 of span, max end notch is 1 7/8". These notches can be on the top or the bottom, but preferred on the top.

This all per minneapolis, MN code:
http://www.ci.minneapolis.mn.us/insp...amemembers.pdf

There are also usually requirments that these notches and holes must have a specified distance between them. Here's another link that'll address some of that:
http://www.ventura.org/vcrma/build_safe/pdf/b-21.pdf

From what you describe, sounds like your plumber did not conform to the standard building codes for your joist size. You should contact your local building code officials since the joist integrity could be compromised. There is a product that may remedy this called the joist reinforcer, though your local inspectors would be the ones to confirm this with. Here's a link that'll show you the details:
http://www.metwood.com/joist_reinfor...ct_details.htm
Reply With Quote
  #6 (permalink)  
Old 01-17-2006, 09:56 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,346
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Kactus - where do you find all these reference web sites? Do you have a list of 'em all? Can you contribute anything from your experiences or do you do nothing but search for answers you can't give?
Reply With Quote
  #7 (permalink)  
Old 01-17-2006, 11:24 PM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
Hazy Old Boy, quite testy are we now! At least my answers are right, with proof to back em up. Looks like I did give the poster his information he was seeking which is more than I can say for you. What the heck did you tell the poster that was of any value to him with his problem? Were you just bored and felt like telling him a 2x is really 1 1/2"? Looks like maybe you're feeling a bit inadequate and hammering me with trivial garb in an attempt to discredit makes you feel better about yourself. Hey, get over it, these folks are here looking for answers and don't need to deal with your personal problems.

PS: Almost forgot, Before you go whinning to the administrator about this post, just remember, you choose this path we're on.
Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Forum Navigation
     > Forum News
     > Illustrations
     > You Gotta Laugh!
     > Catch All
     > Plumbing
     > Electrical
     > Flooring
     > Wall Coverings
     > HVAC
     > Stenciling
     > Appliances
     > Audio & Video
     > Projects
     > Faux Painting
     > Painting
     > Gardening
     > Decks & Fences
     > Outdoor Projects
     > Garage Doors
» Links

» Search

Home Repair Forum
Google   
» Online Users: 19
0 members and 19 guests
No Members online
Most users ever online was 388, 07-01-2007 at 01:54 AM.
Powered by vBadvanced CMPS v2.2.0

All times are GMT -5. The time now is 08:20 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0