return duct size

I am installing a duct work for a ducted aircondition (cold air only).
I am new at this work.

The supplier of the air handler equipment suggested that the return need only be 60% (measured by cross-section) of the supply, but the instruction manuel, which is very brief, says that the duct of supply and return shall not be size smaller than opening on air-handler.

can somebody answer my question or have I omitted pertinant information.

John
Reply With Quote
  #2 (permalink)  
Old 07-16-2004, 06:19 PM
Journeyman
 
Join Date: Nov 2003
Location: .
Posts: 440
Hube is an unknown quantity at this point
I always size the return to be at least 10 % more in area than the the supply. Example; 12 x 18 supply.....12x20 R/A Hube
Reply With Quote
  #3 (permalink)  
Old 07-16-2004, 06:35 PM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
imeduc
You dont say what you have there So you need 400cfm per ton thats like a 3ton you need 1200 cfm. For the duct 70 to 80 sq"
per ton all the time for a good job. So for a 3 ton unit go for 210 to 240 sq" for out and return and it will work very good for you.

ED[B)]

My mistakes dont define me they inform me.
Reply With Quote
  #4 (permalink)  
Old 07-16-2004, 06:50 PM
New Member
 
Join Date: Jul 2004
Location: Belize City, Belize.
Posts: 4
Friesen
thanks for responding
I am installing a barometric by pass damper to compensate for air volume when the zone dampers close. I am planning to divide the airconditioned area in six zone one zone which is 33% of area and the warmest will always be open. Does putting in a barometric bypass damper into the return duct change the way return duct size is calculated? l
Quote:
quote:Originally posted by Hube

I always size the return to be at least 10 % more in area than the the supply. Example; 12 x 18 supply.....12x20 R/A Hube
Reply With Quote
  #5 (permalink)  
Old 07-16-2004, 08:52 PM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
imeduc
You dont say just what you have there. how big how long is the main duct. With out a print I would not say. I find on big jobs it dont pay to go to zone dampers . We dont even like for 10 tons, two 5ton on same duct and 2 stage tstat works a lot better. I have done homes where we have put in 8 heat cool units for zones. Have done large jobs on one 350 ton with 2 of them 22 ton and all the rest 10 and 5 and 3 ton units. Zones are to much work to keep up and like you ask with the bypass just a waste

My .02 cents ED

My mistakes dont define me they inform me.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,148
Threads: 6,795
Posts: 28,085
Top Poster: HayZee518 (3,834)
Welcome to our newest member, fixitdad
» Links

» Online Users: 23
1 members and 22 guests
HayZee518
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 04:17 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0