07-16-2004, 06:00 PM
|
|
|
New Member
|
|
Join Date: Jul 2004
Location: Belize City, Belize.
Posts: 4
|
|
|
return duct size
I am installing a duct work for a ducted aircondition (cold air only).
I am new at this work.
The supplier of the air handler equipment suggested that the return need only be 60% (measured by cross-section) of the supply, but the instruction manuel, which is very brief, says that the duct of supply and return shall not be size smaller than opening on air-handler.
can somebody answer my question or have I omitted pertinant information.
John
|

07-16-2004, 06:19 PM
|
|
|
Journeyman
|
|
Join Date: Nov 2003
Location: .
Posts: 440
|
|
|
I always size the return to be at least 10 % more in area than the the supply. Example; 12 x 18 supply.....12x20 R/A Hube
|

07-16-2004, 06:35 PM
|
|
|
Apprentice
|
|
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
|
|
|
You dont say what you have there So you need 400cfm per ton thats like a 3ton you need 1200 cfm. For the duct 70 to 80 sq"
per ton all the time for a good job. So for a 3 ton unit go for 210 to 240 sq" for out and return and it will work very good for you.
ED[B)]
My mistakes dont define me they inform me.
|

07-16-2004, 06:50 PM
|
|
|
New Member
|
|
Join Date: Jul 2004
Location: Belize City, Belize.
Posts: 4
|
|
thanks for responding
I am installing a barometric by pass damper to compensate for air volume when the zone dampers close. I am planning to divide the airconditioned area in six zone one zone which is 33% of area and the warmest will always be open. Does putting in a barometric bypass damper into the return duct change the way return duct size is calculated?
l
Quote:
quote:Originally posted by Hube
I always size the return to be at least 10 % more in area than the the supply. Example; 12 x 18 supply.....12x20 R/A Hube
|
|

07-16-2004, 08:52 PM
|
|
|
Apprentice
|
|
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
|
|
|
You dont say just what you have there. how big how long is the main duct. With out a print I would not say. I find on big jobs it dont pay to go to zone dampers . We dont even like for 10 tons, two 5ton on same duct and 2 stage tstat works a lot better. I have done homes where we have put in 8 heat cool units for zones. Have done large jobs on one 350 ton with 2 of them 22 ton and all the rest 10 and 5 and 3 ton units. Zones are to much work to keep up and like you ask with the bypass just a waste
My .02 cents ED
My mistakes dont define me they inform me.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 10,148
Threads: 6,795
Posts: 28,085
Top Poster: HayZee518 (3,834)
|
| Welcome to our newest member, fixitdad |
» Links |
|
|
All times are GMT -5. The time now is 04:17 AM.