Hi Rise Condo Thermostat Replacement - Need Help!!
Okay, so I live in a high rise condo building and I want to replace my thermostat. I believe my building is a 4 pipe system. In any case, I need to replace my thermostat because I need a programable thermostat so that I can control my energy bill a bit better. In my building I only pay for the blower and there's really no need to have it on all the time.
So I took off the current thermostat and took it to the local Home Depot. The guy there said that it'd work with something that they had there so I got some programable Honeywell. When I got home and read the instructions, it said that if I had 6 or more wires to not use this unit. My current thermostat has 6 wires connected to a wire harness that then attaches to the blower. Does anyone have any clue as to what kind of thermostat I have to use? Also, how do I know which wire goes where? Do I have to go to a special contractor's store to get something to work?
I live in Chicago so if you know of somewhere to go please let me know! Thanks.
|

02-22-2005, 08:54 PM
|
|
 |
Deity
|
|
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
|
|
|
Would need some additional information...If you are in a high rise condo which receives HVAC from a central machinery room via a 4 pipe system it sounds like you have a Hot & cold deck circulating hydronic system.
What is the wire size of the wires on the present thermostat?
|

02-22-2005, 09:52 PM
|
|
Handyman
|
|
Join Date: Dec 2004
Location: USA.
Posts: 43
Thanks: 0
Thanked 0 Times in 0 Posts
|
|
|
If you are paying for blower operation only, you are not going to see much savings. Probably not worth the trouble.
|

02-22-2005, 10:44 PM
|
|
 |
Deity
|
|
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
|
|
|
Dean is definitely correct in his assesment that there would be little to know actual savings.
An HVAC inside fan motor is typically a 1/4hp motor.
746watts = 1 HP, therefore the motor only uses 746/4= 186.5 watts.
Even if the fan was presently running 100% of the time and you reduced the run time to 50% duty cycle, the actual savings would only be 93.5 watts. It would be definitely more cost effective to simply make sure a couple light bulbs are turned off.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 12,946
Threads: 7,778
Posts: 33,327
Top Poster: HayZee518 (4,978)
|
| Welcome to our newest member, mitchell123 |
» Online Users: 21 |
| 0 members and 21 guests |
| No Members online |
| Most users ever online was 400, 06-22-2009 at 07:11 AM. |
» Links |
|
» Sponsors |
|
|
|
All times are GMT -5. The time now is 05:47 AM.