Furnace Run Then Abruptly Stops

My Goodman (GMS9) gas fired warm air furnace comes on fine--the igniter, the burners, etc. A few seconds of warm air comes thru the registries then the furnace shuts down--it tries to come back on but nothing ignites and it then just winds down. It will do this as long as its allowed to.

If its turned off and sits for a while and is turned back on it will ignite and go thru the whole process and, like mentioned before, a little warm air comes out before shut down.

Any suggestions would be appreciated.
Reply With Quote
  #2 (permalink)  
Old 05-17-2005, 05:31 AM
New Member
 
Join Date: May 2005
Location: Easton, PA, USA.
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
BADCUDA is an unknown quantity at this point
I feel your pain !!! My "Goodman" has left my house cold many times. First thing to check is the circuit board down by the fan. It blinks codes. The codes are on the inside of the bottom door. If that isn't it, clean the probe that extends into the burner on the right side. It gets corroded. Next would come the high limit switch. I've gone thru 3 of them now. Check that stuff first. Good luck.
Reply With Quote
  #3 (permalink)  
Old 05-17-2005, 06:02 AM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
LazyPup has a spectacular aura about
The problem you describe is indictative of a restricted air flow..First check the filter, then chech the return air grilles to see if they are obstructed by furnishings or personal belongings.
Reply With Quote
  #4 (permalink)  
Old 05-17-2005, 08:38 AM
New Member
 
Join Date: May 2005
Location: .
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
BUDMAN is an unknown quantity at this point
The LED blinks 4 times and the inside panel says it is a high limit switch. Any further suggestions?
Reply With Quote
  #5 (permalink)  
Old 05-17-2005, 09:01 AM
New Member
 
Join Date: May 2005
Location: Easton, PA, USA.
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
BADCUDA is an unknown quantity at this point
Exactly what mine did. To test, pull both red leads from high limit switch and connect together. Start furnace and everything should cycle fine. Do not run the furnace like this for an extended period of time. That switch is there for a reason. Buy a six-pack of these switches because they are junk at best. Good luck.
Reply With Quote
  #6 (permalink)  
Old 05-17-2005, 09:24 AM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
LazyPup has a spectacular aura about
The code is telling you it is the high limit switch that is tripping out, but that does not mean the high limit is malfuncioning. If you have a restricted air flow the air in the plenum is getting too hot and causing the high limit to trip out. As i stated before, step one is to check for dirty filters, then check return air grilles to make sure they are not obstructed. Step three is to check the fan motor and blower wheel to insure they are working correctly. The last step is the high limit switch.
Reply With Quote
  #7 (permalink)  
Old 05-17-2005, 10:55 AM
New Member
 
Join Date: May 2005
Location: .
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
BUDMAN is an unknown quantity at this point
Thanks for walking me thru this guys. I'm at step three now--how do I check the fan motor and blower wheel to insure they are working correctly. If everything is o.k. at step three, I'll move on to the limit switch.
Reply With Quote
  #8 (permalink)  
Old 05-17-2005, 08:23 PM
New Member
 
Join Date: May 2005
Location: .
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
BUDMAN is an unknown quantity at this point
Hi everyone--I still need assistance. How do I check the fan motor and blower wheel to insure they are working correctly. Any suggestions will be appreciated.
Reply With Quote
  #9 (permalink)  
Old 05-18-2005, 01:00 PM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
Thanks: 0
Thanked 0 Times in 0 Posts
imeduc is an unknown quantity at this point
Turn the tstat to fan on if it dont run give the blower wheel a spin and see if it runs then

My mistakes dont define me they inform me.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,947
Threads: 7,778
Posts: 33,328
Top Poster: HayZee518 (4,979)
Welcome to our newest member, nolee
» Online Users: 33
0 members and 33 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 10:36 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0