Expanding duct work from 4" to 6"

On top of my furnace are six 4" metal elbow ducts pointing in different direcitons towards the six rooms(no main trunk). I would like to relocate my supply registers in four of these room, from low on the interior wall, to the ceiling at the exterior walls. Would this be a good time to expand the duct work from 4" to 6"? Is there a coupling (w/damper) that exist for this sort of effort?
Reply With Quote
  #2 (permalink)  
Old 06-13-2005, 03:45 PM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
Thanks: 0
Thanked 0 Times in 0 Posts
imeduc is an unknown quantity at this point
Id take the 4" out of the plenum and cut out and put new 6" takeoff in it.

ED

My mistakes dont define me they inform me.
Reply With Quote
  #3 (permalink)  
Old 06-13-2005, 03:53 PM
New Member
 
Join Date: Jun 2005
Location: .
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
Lynn is an unknown quantity at this point
Is that do-able from above in the attic, or would I have to disassemble the plentum from below?
Reply With Quote
  #4 (permalink)  
Old 06-13-2005, 07:06 PM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
Thanks: 0
Thanked 0 Times in 0 Posts
imeduc is an unknown quantity at this point
just where ever you can get to it is all

ED

My mistakes dont define me they inform me.
Reply With Quote
  #5 (permalink)  
Old 06-15-2005, 01:01 PM
Handyman
 
Join Date: Jun 2005
Location: Troy, MI, USA.
Posts: 45
Thanks: 0
Thanked 0 Times in 0 Posts
Umby is an unknown quantity at this point
If I did increase two of the six 4" holes in the plenum up to 6", would I see and increase in cfm to these two rooms? (assuming the same run lengths)
Reply With Quote
  #6 (permalink)  
Old 06-15-2005, 01:34 PM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
Thanks: 0
Thanked 0 Times in 0 Posts
imeduc is an unknown quantity at this point
you should but you dont say what cfm the blower has now. you could kick it up.

ED

My mistakes dont define me they inform me.
Reply With Quote
  #7 (permalink)  
Old 06-15-2005, 03:07 PM
Handyman
 
Join Date: Jun 2005
Location: Troy, MI, USA.
Posts: 45
Thanks: 0
Thanked 0 Times in 0 Posts
Umby is an unknown quantity at this point
How do I know what the cfm is? All I know about this furnace is that it is a Kenmore, 80%AFUE, 2-stage, non-variable, 75000 btu furnace (up flow). I cant find any more specs on it on the web and the installers left me no specs either. Installed with it is a Kenmore central air unit rated at 2-ton. Is this enough info to calculate cfm???
Reply With Quote
  #8 (permalink)  
Old 06-16-2005, 01:22 PM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
Thanks: 0
Thanked 0 Times in 0 Posts
imeduc is an unknown quantity at this point
A 2 ton Ac need 800cfm for it to work ok

ED

My mistakes dont define me they inform me.
Reply With Quote
  #9 (permalink)  
Old 06-16-2005, 02:33 PM
Handyman
 
Join Date: Jun 2005
Location: Troy, MI, USA.
Posts: 45
Thanks: 0
Thanked 0 Times in 0 Posts
Umby is an unknown quantity at this point
So with six 4" ducts, the maximum cfm I am presently getting is:
6 X 25cfm or 150 cfm? (Assuming 6"=100cfm, 5"=50cfm, 4"=25cfm)

I also have four 6" ducts lower on the plenum going off to the newer section of the house, so that's another 400 cfm for a total of:
550 cfm. Is that correct?
Is this a problem, i.e. the 550 cfm ducts vs. the 800 cfm blower?
Thanks Imeduc for your help
BTW
My equipment is all Kenmore

Model#
Furnace: C8MPT075F14A
Condenser: TCA024AKC
Coil: EPD30F15C

I cannot find any specs on these units except for a "Comfortmaker" which I don't think is Kenmore.
Reply With Quote
  #10 (permalink)  
Old 06-16-2005, 06:26 PM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
Thanks: 0
Thanked 0 Times in 0 Posts
imeduc is an unknown quantity at this point
A 6" round pipe is good for 100CFM of air. You might look on the blower door there and see what speed the blower is set on. for heat most are set on MED and for the AC set on HIGH speed

ED

My mistakes dont define me they inform me.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,948
Threads: 7,778
Posts: 33,328
Top Poster: HayZee518 (4,979)
Welcome to our newest member, laniganlosik
» Online Users: 61
0 members and 61 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 12:11 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0