Need to replace HVAC motor

Is this the type of component that can be bought "locally"? One of our AC units was making a lot of noise and so it was switched off. When I got home and checked it out I found the fan to be very stiff. I could turn it by hand but I could definitely not spin it. When the thermostat is switched to COOL the fan does not run and the unit gets HOT! So I have decided that the problem is with the motor and would like to replace it. It doesn't seem like a tricky job so, at this point, I am reluctant to shell out extra money to have someone replace the fan. The tricky part could be getting the part. I could order it online and have it delivered if necessary but if I can get it locally for a couple of bucks more I don't mind supporting local business.

From the motor housing:
208-230V
60Hz
1.03A
1110RPM
1/6Hp
1PH A.O. <--- don't know what this means but I understand all the other numbers.

The motor has a 5" diameter and is attached to the housing via 4 bolts in a square pattern with a diagonal of 4 5/8"

We have 3 units in total and the one that is busted is the one that we don't need to really use as much unless we have guests (which we do as of yesterday).

The capacitor is 5MFD 370VAC. (is that millifarads by the way?)

Cheers, Max


EDIT: by the way, when I say locally I understand that depends on where local is. I should have said can you typically buy this sort of item locally. Local for me is MA by the way.
Reply With Quote
  #2 (permalink)  
Old 06-30-2005, 06:25 PM
Handyman
 
Join Date: Feb 2004
Location: Canada.
Posts: 155
Thanks: 0
Thanked 0 Times in 0 Posts
Rewired is an unknown quantity at this point
Send a message via ICQ to Rewired Send a message via MSN to Rewired
Hey Max!

Yes that part should be EASILY obtainable from any HVAC Supplier or a shop that specializes in electric motor rewinding / rebuilding / or new equipment... Check your local phone directory for one of those shops and take the old one with you so they can easily match up what you have to the equivalent or even something better (more efficient.. better power factor etc.) unless of course you go to a motor shop and its cheaper to have it re-built rather than replaced... Check out all your options.

Oh Ya.. " MfD" on a capacitor stands for Microfarads.. not Millifarads

Good luck!
A.D
Reply With Quote
  #3 (permalink)  
Old 06-30-2005, 06:30 PM
Max Max is offline
Apprentice
 
Join Date: May 2004
Location: .
Posts: 218
Thanks: 0
Thanked 0 Times in 0 Posts
Max is an unknown quantity at this point
Thanks Rewired. I thought milli sounded a little on the large side.

I did another test just now. My earlier report of "I could definitely not spin it" is not 100% true. It can spin but only for about a second after I let it go. When I had my wife switch the thermo to COOL again the fan moved a tiny little bit (only a couple of degrees) and the outside of the unit got HOT real quick. I guess that's why you need a fan. Am I correct in saying that if the unit is getting hot, the fan SHOULD be spinning? That makes sense but since I don't know HVAC that well I can't be 100%.

Cheers, Max
Reply With Quote
  #4 (permalink)  
Old 06-30-2005, 07:04 PM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
LazyPup has a spectacular aura about
That appears to be a very common condenser fan motor but before you begin looking for a replacement there is some additional information you should look for.

Name of Manufacturer

Model Number

Frame Number (The frame number refers to a precise set of industry standards that define the diameter, length, type of mount and other dimensional specifications. (Those dimensions will remain constant regardless of what company made the motor.)

Rotation- defines the direction of rotation when facing the shaft end of the motor. You motor should have an index on the data plate that says either CW or CCW for Clockwise or Counter-clockwise rotation. (Some motors are listed as REV for reversible but that is very unlikely on a condenser fan motor.)

The capacitor you have is a 5MFD which means Micro-Farad, it could also be indicted as 5uF. (The small letter u indicates the latin prefix Micro) Whenever you replace a motor it is best to replace the capacitor at the same time.

Check the SHAFT Diameter and length. Shaft diameter and lenght is critical because the fan blades will mount directly on the shaft and their position in reference to any sheet metal shrouds in the condensing unit are critical.

From the type of mount you describe it sounds like it is bolting directly to the mount plate by the motor housing bolts. Sometimes it is necessary to remove the bolts one at a time and reverse them end for end through the motor to get the excess end of the bolt on the mount end. It is a very simple process of removing a bolt and sliding it through the motor housing from the opposite end and tighening it in place again, then move to the next bolt.

You should be able to find a replacement motor at any local HVAC supply house, or Mill Supply. (Graingers and Johnstone are a couple national suppliers that are quite common in massachusetts.)

The motors are interchangeable between different manufacturers as long as all the specifictaions are the same but I would hesitate to buy a generic name. Try to find one of the well established trade names, GE, Marathon, Dayton Electric etc.

It is always a good practice to replace the capacitor when changing a motor to insure the capacitor is matched to the new motor.

When installing the new motor check the position of the blades on the shaft carefully to insure the blades are properly aligned in the fan shroud. MAKE SURE THE SET SCREW ON THE FAN MOUNT IS REALLY TIGHT.






Reply With Quote
  #5 (permalink)  
Old 06-30-2005, 07:24 PM
Max Max is offline
Apprentice
 
Join Date: May 2004
Location: .
Posts: 218
Thanks: 0
Thanked 0 Times in 0 Posts
Max is an unknown quantity at this point
I'm looking forward to when you get time to write a detailed response LP. Serious, man, great response and I am MOST appreciative.

The info I gave before was just the basics but I do have all the other info noted as well. The manufacturer is / was Magnetek Universal Electric. I have the serial number and model number too. One other piece of info that I found interesting but don't understand is this:

#20 non-det oil every 6 mo. max amb 40o C.

So I have to do "something" with some oil every 6 months and the maximum ambient temp should be 40 degerees C (or 104). Heck, Boston is THAT hot. Still, I don't know what the "something" is.

Thanks, Max
Reply With Quote
  #6 (permalink)  
Old 06-30-2005, 09:39 PM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
LazyPup has a spectacular aura about
#20 non-det oil every 6 mo. max amb 40o C.

That is indicating that the motor bearings should be oiled every 6 months with SAE 20 weight Non-Detergent Oil and the motor is designed to operate in a maximum ambient temperature of 40 deg.C.

As you pointed out, the 40DegC converts to 105degF.

Having formerly lived in the W.Springfield, Holyoke, Chicoppee area I am quite familiar with summers in Massachusetts. It is possible to get the occassional 100 to 105degF day, but for the most part typical summer ambient temps would be closer to the high 90's so that motor is fine.

Allow me to offer you a little tip here as well...

When you get your new motor get some stainless steel non-insulated SPADE connectors to attach to the wires on your new motor to make the electrical connections. The stainless steel connectors cost a few pennies more, but you dont have to worry about corroded connections causing voltage losses.
Reply With Quote
  #7 (permalink)  
Old 06-30-2005, 09:53 PM
SSN596's Avatar
Handyman
 
Join Date: May 2005
Location: San Diego, CA, USA.
Posts: 136
Thanks: 0
Thanked 0 Times in 0 Posts
SSN596 is an unknown quantity at this point
In the electronics industry, the prefix small m usually is milli, large M is mega. Capacitors usually use u for micro.'

In the electric motor trade, you usually see Large M used for Micro...farads, although they sometimes use UF.
Reply With Quote
  #8 (permalink)  
Old 07-06-2005, 01:47 PM
Max Max is offline
Apprentice
 
Join Date: May 2004
Location: .
Posts: 218
Thanks: 0
Thanked 0 Times in 0 Posts
Max is an unknown quantity at this point
http://www.bodoin.com/images/ac_fan.jpg shows the label from the old motor.
Reply With Quote
  #9 (permalink)  
Old 07-06-2005, 03:35 PM
Max Max is offline
Apprentice
 
Join Date: May 2004
Location: .
Posts: 218
Thanks: 0
Thanked 0 Times in 0 Posts
Max is an unknown quantity at this point
Anybody got any (more) tips on picking this up? I just came back from my local Johnstone's and they were unable to help me based on the label (img link above). I'm sure that I can just pop in a direct replacement even if it's not exactly the same specifications but I do know that some specs must be an exact match such as the bolt pattern. I'll try some online places and see what mileage I get there.

Edit: Contacted Grainger and they said the same as Johnstone, that is they can't help. I think the problem is the lack of information on the motor. Johnstone's suggested contacting the manufacturer of the AC unit and see what they say.
Reply With Quote
  #10 (permalink)  
Old 07-06-2005, 05:27 PM
Max Max is offline
Apprentice
 
Join Date: May 2004
Location: .
Posts: 218
Thanks: 0
Thanked 0 Times in 0 Posts
Max is an unknown quantity at this point
Here's the label from the unit.

http://www.bodoin.com/images/heil_unit.jpg
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,946
Threads: 7,778
Posts: 33,345
Top Poster: HayZee518 (4,977)
Welcome to our newest member, mitchell123
» Online Users: 18
1 members and 17 guests
anie_b
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 03:58 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0