Talking Blower Stays On, Heat Does Not

Howdie. Thought you nice folks might be able to give me some advice.

I have a Carrier Gas Furnace (Super Saver 58SSB) that is about 19 yrs old. A few days ago, the relay started clicking non stop trying to light up the furnace. So I turned it off on the thermostat and the gas supply (middle of the night so I didn't want to deal with it). When I turn both on again, this time the pilot light won't even go on and usually the relay would start clicking and start igniting the flames into the burner. I light up the pilot manually (I know it is dangerous..) and got the pilot going (stayed on). However, the clicking from the relay is still missing and no ignition to fire up the burner ..... i could smell a little has ( not sure whether it is from the inlet valve or the pilot). If pilot stays on, does it means the thermocouple is okay?
The voltage to the blower control board was checked (120V) and the reset button was depressed. Is there anything else I should check prior to calling repair service?

On the flipside, I am seriously thinking of replacing the furnace and AC since the current furnace is averaging one outage a year requiring repair. My number one priority is reliability so choices are American Standard and Trane. Any suggestion which model to select?

Thanks a lot.

KT
Reply With Quote
  #2 (permalink)  
Old 04-29-2006, 09:06 PM
pushkins's Avatar
Handy, Man
 
Join Date: Mar 2006
Location: North Carolina
Posts: 516
Thanks: 0
Thanked 2 Times in 2 Posts
pushkins is on a distinguished road
It might sound like a silly question but did you make sure the furnace door is closed correctly, it shouldn't light up if it's open.

I just had my HVAC guys install 4 furnaces in properties we own and my own private residence, we installed Westinghouse 2 stage furnaces at all locations.
The price was a little more than most furnaces but less than some others and we are more than happy with them at all locations.
At my private residence we noticed a saving on gas costs almost immediately by the running of stage 1 and stage 2. Stage 1 being just to hold the temperature at the set level and stage 2 is for dramatic temp. changes like friends coming over for dinner and the doors being opened frequently etc...
Reply With Quote
  #3 (permalink)  
Old 05-05-2006, 10:18 PM
hvacwiz's Avatar
Handyman
 
Join Date: Apr 2006
Location: Ohio
Posts: 65
Thanks: 0
Thanked 0 Times in 0 Posts
hvacwiz is on a distinguished road
The furnace you are talking about i believe has what is called a 3 wire pilot, the clickling you are hearing is coming from the from the gas valve because the pilot contacts are not making propery, there is no cleaning of this part and it will need to be replaced. your blower will turn on when a call for heat is present regardless if you have flame or not, blower is controled by timer on circuit board it will turn on automatically after 45-60 sec after call for heat and turn off 90 sec after call for heat ends.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,582
Threads: 6,939
Posts: 28,884
Top Poster: HayZee518 (4,033)
Welcome to our newest member, sgt york
» Links

» Online Users: 39
0 members and 39 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 10:56 PM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0