I have a water filled baseboard system for home heating. I have two valve controls (Honeywell) not wired yet. one for the upper zone and one for the lower zone. both valve are in the open position. each valve has 2 red and 2 yellow wires not yet connected. I have two programmable thermostats already wired with 2 wires red and yellow. one in the upper level of my house one in the lower level. Right now only the lower level is connected to the system. what I would like to do is finish wiring the system for 2 independant zones. There is a transformer (Honeywell Control Circuit Transformer) for the system in place but not wired yet to the boiler or thermostat but it is powered (wired) by 110 volt. Right now there is a wire coming from my programmable thermostat (red and yellow) that connects to a wire from my williamson gas boiler (red and yellow), the heating system is currently working but as 1 zone. what must I do to finish wiring for a 2 zone system. the wiring for the 2nd programmable thermostat is all ready here next to the transformer it is just not hooked up to anything. I need step by step help, thank you for any help you can give me.

Last edited by bigrick7; 05-01-2006 at 01:20 AM..
Reply With Quote
  #2 (permalink)  
Old 05-02-2006, 05:25 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,978
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
just follow the wiring of the first zone
Reply With Quote
  #3 (permalink)  
Old 05-04-2006, 06:58 PM
New Member
 
Join Date: Sep 2004
Location: .
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
bigrick7 is an unknown quantity at this point
the first zone is not hooked up and locked in the open position. the thermostat runs directly to the boiler. the zone valves are not connected and there is nothing connected to the step down transformer. the thermostat is programmable and runs on batteries
Reply With Quote
  #4 (permalink)  
Old 05-04-2006, 09:51 PM
New Member
 
Join Date: Sep 2004
Location: .
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
bigrick7 is an unknown quantity at this point
from what i researched this is what I got so far. I first disconnect the thermostat that is directly hooked up to the furnace. I then take a wire from the R Terminal of both thermostat and connect them to the transformer R Terminal. I then take The second wire from the W Terminal of both thermostat and connect them to there own zone valve (red wire). I have 2 red and 2 yellow on each zone valve(Honeywell). I assume the 2 red are hot and the 2 yellow are end switch Wire. I then take the remaining red wire, 1 from each zone valve and connect that to the C terminal on the transformer. I then take the remaining yellow wire from the zone valve and connect them to the furnace were the original thermostat wire was. is this correct or am I wiring it wrong. thanks again for the help.
Reply With Quote
  #5 (permalink)  
Old 05-10-2006, 09:32 PM
New Member
 
Join Date: Sep 2004
Location: .
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
bigrick7 is an unknown quantity at this point
any help anyone?
Reply With Quote
  #6 (permalink)  
Old 05-15-2006, 05:57 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,978
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
the zone valves have a small heater inside which opens the valve. the other two wires operate a switch that closes when the valve is open. these two wires go to the burner control which fires up the burner. there is a current rating on the zone valve which you use to set up the heat anticipator on the thermostat.
one side of the transformer is a common lead, the other, consider a "hot." (low voltage - 24 volt) wiring is such. one red wire on the zone valve to the common. from the transformer "hot" to the thermostat. return from the thermostat to the other red wire. two yellow wires to the TH terminals on the burner control
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,946
Threads: 7,778
Posts: 33,327
Top Poster: HayZee518 (4,978)
Welcome to our newest member, mitchell123
» Online Users: 20
0 members and 20 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 06:50 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0