A/C runs "forever".

I'm thinking I have a bad thermostat. Can you confirm?

I have a 90s vintage Robertshaw digital programable thermostat. I have the A/C temp set at 78 deg. The A/C will come on and stay on for what seems like forever - up to 3 hours. If I let it go it will take the room temp down to 72-73 degrees before it shuts off. The strange thing is the temp indication on the display will rise up to 80 deg then slowly fall back to 77 deg before it shuts off.

Using two indoor outdoor thermometers, I taped the probe of one one inch below the case of the thermostat. I inserted the other probe inside the thermostat case. Sure enough, when the A/C turned on the temp inside the thermostat immediately started rising and stabilized at 81 deg. The temp on the outside of the case slowly fell to 73 deg. It appears something is creating heat in the thermostat making the A/C stay on.

I blew it out with compressed air and adjusted the "temperature variance thing" with no luck. Bad t-stat? What do you think?

Last edited by Needaclue; 05-18-2006 at 09:39 PM..
Reply With Quote
  #2 (permalink)  
Old 05-19-2006, 09:19 AM
Journeyman
 
Join Date: Nov 2003
Location: .
Posts: 445
Thanks: 0
Thanked 0 Times in 0 Posts
Hube is an unknown quantity at this point
Make sure the wall cavity area that the T stat is mounted on is well insulated, so it is not influenced by any air from above or below.
Reply With Quote
  #3 (permalink)  
Old 05-20-2006, 01:51 AM
Needaclue's Avatar
Handyman
 
Join Date: May 2006
Location: Southern Cal
Posts: 29
Thanks: 0
Thanked 0 Times in 0 Posts
Needaclue is an unknown quantity at this point
Couldn't get into the wall to see how well its insulated so I pulled the thermostat away from the wall and redid the test. Same result. Temp inside thermostat started rising when A/C came on.
Reply With Quote
  #4 (permalink)  
Old 05-20-2006, 09:10 AM
Journeyman
 
Join Date: Nov 2003
Location: .
Posts: 445
Thanks: 0
Thanked 0 Times in 0 Posts
Hube is an unknown quantity at this point
So now that you are sure that the T stat is not picking up heat from the wall cavity means it is definitely a fault in the T stat.
Since you say it is a 90's "vintage" t stat, Maybe its days of service are over.(worn out)
Best to just bite the bullet and spring for an newer one.
Reply With Quote
  #5 (permalink)  
Old 05-21-2006, 06:48 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
inside the stat is a small resistor which is heating up creating the inside temperature difference. called the heat anticipator it is used to anticipate the rise or fall of temperature as the setpoint is reached. try and see if the setting matches the millivolt current on the circuit it's used in.
Reply With Quote
  #6 (permalink)  
Old 09-19-2006, 04:18 AM
Needaclue's Avatar
Handyman
 
Join Date: May 2006
Location: Southern Cal
Posts: 29
Thanks: 0
Thanked 0 Times in 0 Posts
Needaclue is an unknown quantity at this point
Sorry. Thought I answered this long ago. Bought a new T-stat and all is well now. Got one of those fancy touch pad type (Lux). Working great. Thanks for the input.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,944
Threads: 7,777
Posts: 33,327
Top Poster: HayZee518 (4,977)
Welcome to our newest member, Peabarter
» Online Users: 29
1 members and 28 guests
hvacwiz
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 12:00 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0