The three terminal capacitor in the photo is a dual capacitor. Rather than having a separate capacitor for both the fan motor and compressor motor they have built both capacitors into a common canister.

If you examine the top of the capacitor you should find the letters "H" and "F" stamped into the metal housing near the base of the two end terminals. The letter "H" stands for "Hermetic Compressor" and the letter "F" indicates the "Fan motor". The center terminal is then common to both capacitors.

Before you begin testing you must disconnect the main power to the condensing unit, then disconnect the wires to the capacitor.

Technically speaking you should have a large value resistor to short the terminals of a capacitor, but commonly we use a large flat tip screw driver. In the case of the dual capacitor you would first discharge one capacitor then the other by touching a screwdriver from one end terminal to the center terminal, then repeat the process on the opposite end to center. Having done so, you then test each capacitor individually using an ohm meter and the procedure defined above to check from an end terminal to the center terminal to check one capacitor, then repeat the process from the opposite end to center to check the second capacitor.
Reply With Quote
  #12 (permalink)  
Old 08-06-2006, 10:34 AM
New Member
 
Join Date: Aug 2006
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Canti is on a distinguished road
Gotcha... Thanks alot!
Reply With Quote
  #13 (permalink)  
Old 08-09-2006, 04:32 PM
New Member
 
Join Date: Aug 2006
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Canti is on a distinguished road
Sorry to bother you again LazyPup, but when I test my capacitor what setting should I set my analog meter to? I use digital meters all the time so I am a little bit hazy when it comes to analog. Is it the Rx10,000 setting or the Rx1 setting? Is it the Rx1 the highest value setting?

Thanks again.
Attached Images
File Type: jpg meter.jpg (84.8 KB, 3 views)
Reply With Quote
  #14 (permalink)  
Old 08-10-2006, 06:34 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,033
Thanks: 0
Thanked 4 Times in 4 Posts
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
R times 1 or R x 1. this feeds the 9 volt plus 1 1/2 volts off the battry into the cap. tripplet meters use a 9 volt plus a 1 1/2 volt battery in its test circuits.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,582
Threads: 6,939
Posts: 28,884
Top Poster: HayZee518 (4,033)
Welcome to our newest member, sgt york
» Links

» Online Users: 37
1 members and 36 guests
jnaas2
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 11:20 PM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0