Trane XE Furnace Problem

I have a furnace that has a hot surface igniter and will turn red and you can hear the gas valve open. The flames will only stay on for about 3-5 seconds and go out. This happens about 4-5 times and the fan will start. The only way I can possibly get the furnace to keep running without the flames going is set the thermostat below room temperature and bring it back up to a higher room temp. What could be wrong? The pressure switch works!

Help

Joe
Reply With Quote
  #2 (permalink)  
Old 11-15-2003, 07:18 AM
New Member
 
Join Date: Oct 2003
Location: Fair Haven, MI.
Posts: 17
Thanks: 0
Thanked 0 Times in 0 Posts
a46geo

You are re-setting an electronic safety lock out when you do this.

You can do the same thing by turning the furnace switch off and then back on. Although the burner is lighting, a sensor is not detecting the flame. Either a loose connection, a weak sensor or a circuit board is most likley the problem.

Reply With Quote
  #3 (permalink)  
Old 11-15-2003, 09:52 AM
New Member
 
Join Date: Nov 2003
Location: Kearney, MO, USA.
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
airplanejoe
Can you jumper out the flame sensor for a short period to eliminate or prove that the problem is the sensor?

Joe
Reply With Quote
  #4 (permalink)  
Old 11-30-2003, 09:24 PM
New Member
 
Join Date: Nov 2003
Location: .
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
johngrider
I am having a somewhat similar problem with my XE-90. The purge pump will run for about 30 seconds, nothing happens, starts again about 15 seconds. Cycle repeats and repeats. Does maintain the selected temperature on the thermostat. It appears tha the vacuum is insufficient to activate the switch to trigger the igniter. I have reset the thermostat(HONEYWELL PROGRAMMABLE) and it has cycled normally. Does the pressure switch have a designed in bleed? It appears that it has. If I actuate it manually(mouth) all seems to work?
Reply With Quote
  #5 (permalink)  
Old 12-14-2003, 05:23 PM
New Member
 
Join Date: Nov 2003
Location: .
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
johngrider
Follow-up to my prfevious post on XE90. Have verified that all air vents and condensate draines are not clogged. Could only get heat occasionally without pinching off the vacuum line to the back side(away from furnace) of the pressure switch (SWT 1612 replacement is SWT 2523). Decided to plug this line with a golf tee and all seems to work properly. Holds temperature and recovers from 65* at night to 72* at 7:30 am programmed. Don't see any unsafe conditions by doing this but don't understand why it works. Talked to another member that has a XE-90 and he did the same thing and his is working also. He had a technician replaced this vacuum switch without any change in performance. Question is "WHY DOES IT WORK WITH THIS LINE PLUGGED AND WHAT DO I DO NEXT?? Any help and comments would be appreciated.

John
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,582
Threads: 6,939
Posts: 28,884
Top Poster: HayZee518 (4,033)
Welcome to our newest member, sgt york
» Links

» Online Users: 39
0 members and 39 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 10:52 PM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0