    Bryant troubleshooting help

    I'm getting near the end of my rope, but luckily I found this forum (and intend to explore others as time allows).

    I've got an early '90s Bryant Plus 90, Model398AAZ06060AAKA. It worked flawlessly up until two years ago, when it started to intermittantly not start up, but let me explain. In the sequence of events, no one (myself or any furnace repair guy) has ever been able to witness for the sake of troubleshooting what exactly takes place (the nature of intermittant), but here is the outline:

    The inducer motor/fan will start up in response to the thermostat, but it quits before the burner ever comes on. Whether or not the pilot light makes it on is anybody's guess. This apparently puts the electronics into a lockout mode. If you switch off the furnace, either with the main power switch (furnace mounted) or at the thermostat, then switch back on, it will come back and start over, this time successfully. The furnace will work normally for anywhere from 24 hours to two weeks, then will fail again, whereupon you can reset it with the power off/on routine and go from there, with the results being another undetermined length of normal service.

    The service people who've work on this thing have kind of come to an impass, and I've educated myself on the sequence of operations, based on the manuals that came with the furnace, so I could do my own troubleshooting, as I have a background in electronics. Not that I have anything against service people, but it has simply become a matter of parts swapping, as they don't seem to have any broad history of this particular problem to go by (plus it's expensive!), so I've turned to the 'Net to see who might be able to help.

    Let me also say that, along the same time this problem started to develop, a leak in the secondary heat exchanger was detected (water in the blower compartment and then on the floor -- never to any level that would immerse the electronics), and that was replaced recently.

    The service techs started out checking the inducer intake for obstructions -- no problem there. Then they swapped out the ignitor/lockout module (ILO -- a logical choice as I've come to learn). But because the furnace never fails in the presence of anyone (could take weeks), they pack up and consider it solved, until we call again. Generally, if someone is home, we just switch off/on the furnace and keep the house warm. The ILO has been changed twice!

    Then the following parts have all been replaced: The inducer motor relay board; the pressure switch; the inducer motor itself (which, when it didn't solve the problem, they swapped back out for the old one, fortunately for me); the thermostat itself; the pilot assembly; the blower control PC board. I also, on a hunch, decided recently to bypass (put a jumper on) the high-temp limit switch, thinking that this might have become degraded due to the water possibly being blown around in the blower compartment from the leaky exchanger. Nope. It still fails and must be reset with the off/on routine.

    The only thing left I can think of is that there's a problem in the redundant gas valve, perhaps with the opening of the pilot gas flow, but that's why I'm here today, folks. Keep in mind, the inducer motor seems to shut off early in the sequence, before the burners are ever on (that's what I keep trying to assess, but I'm never there or paying close enough attention when it shuts off).

    Does anyone have a clue what might be going on with this thing? I'm not inclined to have the gas valve replaced unless the evidence is strong (mucho dinero, you see). I know the problem must be electrical/electronic in nature, but practically every part has been replaced. Has anyone ever had a problem with the 115VAC/24VAC transformer becoming intermittant? Haven't replaced that part yet. Or any electrical connectors becoming corroded, perhaps just a ground connection? Things in both compartments actually look pretty clean.

    Aren't there any diagnostic devices devised that can be connected up to this to more closely pinpoint the area of trouble? That would be a good electronics class project!

    I need help, or I may have to get a new furnace, which the two local outfits that sell/service Bryant would love to provide! But really, this has got to be something so simple. Everything else works fine on it, and it's only 15 yrs. old or so. Just a baby, really. But the services techs can't apply themselves in this sort of a problem for any length (understandably), so I'm trying to find out the fix myself. HELP!

  2. #2
    HayZee518's Avatar
    HayZee518 is offline Deity
    Join Date
    Jul 2004
    Location
    Saint Regis Falls, NY, USA.
    Posts
    8,390
    Thanks
    1
    Thanked 460 Times in 447 Posts
    how about the flame detector? once the pilot is on, the flame sensor detects the flame and opens the valve. if it is a millivolt thermopile generator, perhaps it isn't providing the 500 millvolt output to the main valve. on the millivolt line inside the valve is an insulator and a copper button. if the insulator is shot or near shot sometimes you'll get the low voltage and the valve operates normal. other times the output shorts out and the pilot never lights.

  3. #3
    whacker is offline New Member
    Join Date
    Dec 2006
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    As I understand it, flame detection is accomplished on the modular pilot assembly; it's part of the unit that was replaced when the service tech changed that part. I could be wrong, but that's the way it looks, and also as it appears on the schematic I have of the furnace. If you know different to a certainty, please elaborate. I'm getting desparate.

    And thanks for your reply! You're the only one so far.

  4. #4
    HayZee518's Avatar
    HayZee518 is offline Deity
    Join Date
    Jul 2004
    Location
    Saint Regis Falls, NY, USA.
    Posts
    8,390
    Thanks
    1
    Thanked 460 Times in 447 Posts
    send me a copy of the schematic - maybe I can see something you are bypassing.

  5. #5
    whacker is offline New Member
    Join Date
    Dec 2006
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    That's going to be difficult, as I don't have a scanner available. Maybe I can borrow one, but it'll be a few days...

  6. #6
    cfwolnia is offline New Member
    Join Date
    Dec 2006
    Posts
    1
    Thanks
    0
    Thanked 1 Time in 1 Post

    90 plus

    Hi, I have a similar furnace (Bryant 90 Plus) from early to mid 90's. Not sure about the model #, but on mine if I pop off the cover, there are two round plugs about the size of a half dollar. Behind one of those is an LED that flashes with an error code. Look in your manual to see what the cause is.

    I had a similar problem recently, where she acted like she was going to fire up, but then shut off. Turned out it has a sensor that checks the airflow. In my case (and I would guess in yours too) I had a dirty filter which restricted proper airflow. I didn't have a new one on hand, so I simply vacuumed the old one and put it back in. Ran it that way for about a month before finally replacing the filter.

    Don't know if this will help you, but good luck!

  7. The Following User Says Thank You to cfwolnia For This Useful Post:

    akbob49 (01-20-2011)

  8. #7
    whacker is offline New Member
    Join Date
    Dec 2006
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    cfw-

    The only filters on mine are the main furnace airflow filters, and they're fine. They sit outside the unit where the return airflow comes in. Mine is an upflow style unit.

    However, I did discover that the high temp limit switch (sensor) might have been worth checking out. It is in the internal airflow (near the heat exchangers). I made a little jumper to "go around" it, and for a few days I thought it was doing the trick, but no, eventually (within two days), it stopped coming on again. But I turned her off, and back on, and she fired right up and ran for eight days before failing again.

    CFW, if your unit has a diagnostic LED, maybe it's a Plus 90i model. That's a generation newer than mine. Mine has a one speed AC motor for the main blower, and the control electronics are run from a 24 volt AC transformer tap. No microprocessors. How large was this "filter" you're referring to, and whereabouts was it located?

    I still am leaning to the idea that it's the redundant gas valve (it's the only part that hasn't been replaced - unless the sevice tech or I missed something). There are two servos or relay operated valves on it, one for the pilot and one for the main gas burner. It's either that or some really obscure electrical connection problem, corroded or loose connection.

    I was trying to get a scanner to send images from my owner's manual over to HayZee518, but that turned out to be a no-go, so I'll probably have to go to Kinko's and scan the schematic so I can send it. We'll see. It's been mild out here in Michigan up 'til now, but that can't last forever!

    Thanks for your input, though. I'll keep you posted!

  9. #8
    Joe_Shmo is offline New Member
    Join Date
    Dec 2006
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Simular Bryant Problem

    Whacker,

    I have a mid 90's Bryant +90 natural gas furnace. I recently experienced a similar issue to which you have described. When the thermostat would call for heat the furnace vacuum motor would come on followed by the thermo igniter. Once the igniter would get hot "orange" I could hear the gas valve click and turn on and what I think is the sound of gas flowing. However, after about 8 seconds no combustion would occur and the gas valve would shut off. The furnace would retry 2 more times and then shut down in a lockout mode for 3 hours.

    The problem with my unit was in the gas valve. Even though the valve would turn on there was insufficient gas flow sometimes. I ended up removing the brass plug on the gas valve and turning "in" the flame adjustment to let more gas into the combustion chamber. If you try this you need to be careful to not turn it up too high or else the thermo switch will trip stop the unit from turning on until it is manually rest.

    I hope this helps,

  10. #9
    leone184 is offline Handyman
    Join Date
    Jan 2005
    Location
    Fairport, New York, USA.
    Posts
    56
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Smile furnace problem

    This sounds like a problem my furnace was having. It turned out to be the flame-senser. For some reason the senser did not register that the gas jets were ignited (they were). This made the furnace think the jets were releasing gas that was not being burned. This would shut down the cycle after about 60 seconds. The senser looks like a thin gray rod of metal with a porcelain cap, and a wire sticking out of the top. The rod itself sticks down thru a hole in the frame, and right in front of one of the jets.
    Every year before the winter season, I have to remove the rod and run it through the wire brush on my bench grinder. It does not look dirty or have any noticible carbon build-up on it, but the cleaning seems to last the entire season with no other problems.

    I hope this helps.
    leone184

  11. #10
    wlc0216 is offline New Member
    Join Date
    Jan 2007
    Location
    Portage, MI
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Bryant Plus 90i

    My furnace is not running properly. When it goes through the start up process, the gas valve opens and flames for a short period then I hear a clicking and notice puffs of air from the combustion chamber and the gas valve shuts down. This process repeats continuously. I checked for a flame sensor as described by the previous posting but there is no such rod with a wire attached positioned infront of the flame area.

    I checked on the error code displayed and it was 3 amber flashes followed by 1 green flash. I am hoping to repair it myself and would appreciate some advice.