Furnace/Thermostat Issue

I have a Carrier Furnace, three years old. Installed a Hunter thermostat last year model 44260 - programable. Electronic pilot.

At least once a day in early morning and evening, the furnace blower will activate, the pilot comes on and then shuts off in about 5 seconds. While the blower keeps going, the pilot and or flame will come on for another 5 seconds and goes out. After about 5 tries all stops. However, the thermostat does not kick on heat as it should and then I have to activate system by either shutting off blower swith on furnace or open and close the front cover to activate blower. I have another emergency switch in hallway, which also activates blower on and off and activates system. If I don't do this, the furnace doe snot come at all. I changed batteries and filter and checked door on furnace but it is secure.Thermostat had done this earlier in season and it stopped but now it does it every day. Once I activate blower, furnace works for about 12 hours with no problem.

Please advise.

Thanks

Pashue
Reply With Quote
  #2 (permalink)  
Old 01-24-2007, 04:25 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,343
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
check out the "hot surface" ignitor. this unit almost relies on its resistance to operate. I had one in my propane stove oven that gave me problems. the wire connectors came loose so I crimped on another only to have it give way in a few days. so I used a nickel silver crimp on. this lasted about six months then problems again. I removed the ignitor only to have it catch on something and it broke into a million pieces. bought a new one for 15 bucks, installed it and haven't had another problem with it in four years!
Reply With Quote
  #3 (permalink)  
Old 01-25-2007, 06:24 AM
New Member
 
Join Date: Jan 2007
Posts: 12
pashue is on a distinguished road
HayZee518

I will look into this as it sounds as though it could be the problem. And, I did look this part p on Internet and it notes it only lasts for 3-5 years and breaks as often sometimes as a light bulb. My wife informs me our furnace is actually 6 years old not 3!
Just one question for clarification - why would the thermostat/furnace work all day long but, then have this problem around 3-4:00 A.M. If it is broke, shouldn't it not work at all? Is it because is just gets too hot and then stops working? Could it be the program mode in thermostat be corupt during the nightime phase or a resistor or part inside is faulty? It happened again this morning.

Thank you much!

Pashue
Reply With Quote
  #4 (permalink)  
Old 01-25-2007, 06:43 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,343
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
the hot surface ignitor operates on 120 volts and the thermostat is 24 volt - so there isn't a problem between the stat and the ignitor. the terminations for the ignitor needs to be tight, a loose condition will change the resistance of the unit. another new fangled safety feature. in this case the main gas valve is current sensitive and operates off the ignitor's resistance. the old formula for current is amps equals volts divided by resistance. 120 / 60 ohms = 2 amps. 120 / 40 ohms = 3 amps. 120 / 20 ohms = 6 amps. so if the main valve is seeing other then what current is meant for it - it will not open.
Reply With Quote
  #5 (permalink)  
Old 01-26-2007, 01:56 PM
New Member
 
Join Date: Jan 2007
Posts: 12
pashue is on a distinguished road
ok, I understand now.

Thanks for your help, I really appreciate it!

Pashue
Reply With Quote
  #6 (permalink)  
Old 01-26-2007, 11:21 PM
lonestarheir's Avatar
Handyman
 
Join Date: Jul 2005
Location: Lancaster, Texas, USA.
Posts: 136
lonestarheir is an unknown quantity at this point
Send a message via Yahoo to lonestarheir
In the past I have seen a lot of problems with the hunter thermostats, and I know this sounds weird, but especially when installed with carrier furnaces. My company is a Factory Authorized Dealer for Carrier so I run. Into this problem every so often. If it were me I would try a different brand of stat and make sure that it is wired correctly by cross referencing the thermostat wiring diagram and the furnace control board diagram which can be found at www.carrier.com. You wl just need a model, series, and serial number to get it.

Hope this helps.
__________________
__________________________________________________

Brandon
- Have you changed your filter this month? -
Reply With Quote
  #7 (permalink)  
Old 01-29-2007, 05:29 AM
New Member
 
Join Date: Jan 2007
Posts: 12
pashue is on a distinguished road
Dear lonestarheir:

Two years ago I changed the original thermostat with a Honeywell. It had problems too so, last year I bought this Hunter.

Yesterday, while I was trying to find where the surface heat ignitor is located (still can find it and will have to find manual to see where it is - inside cover data is so small I'll need a magnifying glass to read it) I noticed the front cover was loose on the bottom when removing it. It took me a while to get it on correctly. That was at 1:30 P.M. So far it is working but as stated previously, I will have to wait at least 20 hours to see if it stops working again. I did place thermostat to manual settings on Saturday but it still shut down after 20 hours.

I will probably try another thermostat if the ignitor looks ok. I believe I have thermostat wired properly or it would not have worked for almost a year - wouldn't it?.

Thanks.

Pashue
Reply With Quote
  #8 (permalink)  
Old 01-30-2007, 03:44 PM
New Member
 
Join Date: Jan 2007
Posts: 12
pashue is on a distinguished road
Well, the furnace is working fine now! I believe the problem was with the furnace cover where shut-off switch sits. I also re-set the thermostat so, I do not know 100% which was the fault.

Thank you both for all your advice. I am sure it will come in handy should I experience a similar problem.

Pashue
Reply With Quote
  #9 (permalink)  
Old 01-31-2007, 05:36 AM
New Member
 
Join Date: Jan 2007
Posts: 12
pashue is on a distinguished road
Hey guys,

Its, BACK!!!!!!!

Worked great for two whole days

So, I've checked some other sites with same problem - even with Carrier furnace and their own thermostat. Each division of Carrier blames each oher.

Now, I am going to do both - change thermostat and/or replace the surfface heat ignitor. Can someone explain where SHI is located? The only wire to area where blower and coils are, is a thing that looks like the ceramic cylinder like that of the ingitor of a gas grill that makes the spark. But there are no screws or a method of removing. Is it behind this? My area to work is limitted and I need my skinny son to actually get in there to pull cover, etc. Furnance is directly in front of water heater. Poorly built house!!!

Thanks.

Pashue
Reply With Quote
  #10 (permalink)  
Old 01-31-2007, 06:07 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,343
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
look for a round spring clip like a washer with internal "ears" it fits around the ignitor. the ignitor pushes up through a hole and the spring clip holds it in place. you'll need a screwdriver to pry up this spring clip.
Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Forum Navigation
     > Forum News
     > Illustrations
     > You Gotta Laugh!
     > Catch All
     > Plumbing
     > Electrical
     > Flooring
     > Wall Coverings
     > HVAC
     > Stenciling
     > Appliances
     > Audio & Video
     > Projects
     > Faux Painting
     > Painting
     > Gardening
     > Decks & Fences
     > Outdoor Projects
     > Garage Doors
» Links

» Search

Home Repair Forum
Google   
» Online Users: 19
1 members and 18 guests
Psycho0124
Most users ever online was 388, 07-01-2007 at 01:54 AM.
Powered by vBadvanced CMPS v2.2.0

All times are GMT -5. The time now is 01:07 AM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0