Blower won't run?

Hi everyone!

Relative Noob here with another furnace question. I have a Standard furnace with an electronic ignition, only about 6 or 7 years old. About 6 months ago I replaced the blower motor and capacitor as they had frozen up. So I don't believe they are the source of the current problem. Filter is ok, too.

When my T-stat calls for heat, the furnace starts its "cycle" - draft fan starts, ignitor heats up, the gas valve opens and the furnace lights, but the blower does not come on. It runs this way for a minute or two, then shuts off. There's an LED that flashes its trouble code, which when translated says "OPEN HIGH LIMIT DEVICE". I found 2 limit switches in the start circuit according to the schematic on the door. I have jumpered across both in a effort to determine which has failed, with no luck. I cleaned the flame sensor and have continuity across the pressure switch and the 2 limit switches, and still no blower motor start. I jumpered in 120V to the blower motor, and it works fine.

Where else to look? Thanks in advance...

Scatterbrained
Reply With Quote
  #2 (permalink)  
Old 03-12-2007, 06:43 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,033
Thanks: 0
Thanked 4 Times in 4 Posts
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
send me a copy of the wiring schematic - hayzee - srf12980@localnet.com.
Reply With Quote
  #3 (permalink)  
Old 03-13-2007, 01:25 AM
lonestarheir's Avatar
Handyman
 
Join Date: Jul 2005
Location: Lancaster, Texas, USA.
Posts: 137
Thanks: 0
Thanked 0 Times in 0 Posts
lonestarheir is an unknown quantity at this point
Send a message via Yahoo to lonestarheir
Quote:
Originally Posted by scatterbrained View Post
Hi everyone!

Relative Noob here with another furnace question. I have a Standard furnace with an electronic ignition, only about 6 or 7 years old. About 6 months ago I replaced the blower motor and capacitor as they had frozen up. So I don't believe they are the source of the current problem. Filter is ok, too.

When my T-stat calls for heat, the furnace starts its "cycle" - draft fan starts, ignitor heats up, the gas valve opens and the furnace lights, but the blower does not come on. It runs this way for a minute or two, then shuts off. There's an LED that flashes its trouble code, which when translated says "OPEN HIGH LIMIT DEVICE". I found 2 limit switches in the start circuit according to the schematic on the door. I have jumpered across both in a effort to determine which has failed, with no luck. I cleaned the flame sensor and have continuity across the pressure switch and the 2 limit switches, and still no blower motor start. I jumpered in 120V to the blower motor, and it works fine.

Where else to look? Thanks in advance...

Scatterbrained

Sounds like you have a bad fan relay, which would explain why it will run when you hook the motor up directly to 120V
__________________
__________________________________________________

Brandon
- Have you changed your filter this month? -
Reply With Quote
  #4 (permalink)  
Old 03-13-2007, 01:43 AM
New Member
 
Join Date: Mar 2007
Location: Shorewood, IL
Posts: 5
Thanks: 0
Thanked 0 Times in 0 Posts
scatterbrained is on a distinguished road
schematic

Schematic is posted on the back of the panel. Tough to email that...
Reply With Quote
  #5 (permalink)  
Old 03-13-2007, 01:45 AM
New Member
 
Join Date: Mar 2007
Location: Shorewood, IL
Posts: 5
Thanks: 0
Thanked 0 Times in 0 Posts
scatterbrained is on a distinguished road
Fan relay

How do I test the fan relay? I didn't see it in the prints, or for that matter anywhere in the wiring. Is this on the circuit board? I read somewhere that the Standard (Trane?) circuit boards have a habit of failing. How much would a new one cost?

S
Reply With Quote
  #6 (permalink)  
Old 03-13-2007, 04:15 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,033
Thanks: 0
Thanked 4 Times in 4 Posts
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
fan relay is a little gizmo about the size of a pack of cigs - brown or wine colored. if you can access the crossbar, the part that holds the contacts, use an insulated probe and push the crossbar in. this should start the fan. in its base you should see two terminals coming out of the coil. control voltage is probably 24 volts. if you have a meter connect the probes across the coil and when the unit is functioning regularly you should read 24 volts. you then found your culprit with a burned out coil. shut off the power, mark the wires and take it out and get a replacement.
Reply With Quote
  #7 (permalink)  
Old 03-13-2007, 08:10 AM
New Member
 
Join Date: Mar 2007
Location: Shorewood, IL
Posts: 5
Thanks: 0
Thanked 0 Times in 0 Posts
scatterbrained is on a distinguished road
Fan relay?

I don't see anything that looks like a fan relay. This doesn't show up on the schematic either. Help!
Reply With Quote
  #8 (permalink)  
Old 03-13-2007, 08:18 AM
Java_Bob's Avatar
Handyman
 
Join Date: Sep 2006
Posts: 132
Thanks: 0
Thanked 0 Times in 0 Posts
Java_Bob is on a distinguished road
does anything happen if you place the thermostat in fan on (instead of auto)??
Reply With Quote
  #9 (permalink)  
Old 03-13-2007, 08:58 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,033
Thanks: 0
Thanked 4 Times in 4 Posts
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
I recall a previous post about a trane blower that I was able to help the user - only his problem was the fan wouldn't stop. Look for a circuit board about 2 inches by three inches. on this is a relay - part number WW24X0224. Get a replacement and your problems should be over. go to the trane site and find a dealer near you.
on the board it should say FDR

Last edited by HayZee518; 03-13-2007 at 09:00 AM. Reason: failed to list board nomenclature
Reply With Quote
  #10 (permalink)  
Old 03-30-2007, 02:12 PM
New Member
 
Join Date: Mar 2007
Location: Shorewood, IL
Posts: 5
Thanks: 0
Thanked 0 Times in 0 Posts
scatterbrained is on a distinguished road
Fixed

Found an open limit switch on the circuit board. Ended up replacing the whole board for $75. On the plus side, the Father in law fixed the board, so I now have a spare, just in case!

S
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,582
Threads: 6,939
Posts: 28,884
Top Poster: HayZee518 (4,033)
Welcome to our newest member, sgt york
» Links

» Online Users: 26
0 members and 26 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 11:40 PM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0