09-12-2007, 01:17 PM
|
|
|
New Member
|
|
Join Date: Sep 2007
Posts: 4
|
|
|
Aquastat for Peerless Boiler
Help Me Please!!
I need to replace the aquastat on my 1980 peerless boiler. The description is: Honeywell R8182D 1012. Everywhere I have looked, and all the people I have talked with say this unit never existed with the 1012 extension. When I ask for a replacement, they say I can not get a replacement without a crossreference to the 1012, which they say doesnt exist. This is a catch 22.
Can someone out there tell me if Honeywell R8182D 1079 will work in this application? That is the closest thing that I can find
Thanks,
Jesse East
|

09-12-2007, 02:43 PM
|
|
|
 |
Deity
|
|
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,211
|
|
|
Your looking at the wrong end of the problem.
Get the model number off your Peerless boiler and have your supplier see what aquastat it requires.
|

09-14-2007, 09:54 AM
|
|
|
New Member
|
|
Join Date: Sep 2007
Posts: 4
|
|
|
You are so right. Here is the info::: Peerless JO-4 WPCT JO-56012.
Can anyone help determine the required aquastat?
Thanks
Jesse East
|

09-14-2007, 02:02 PM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,841
|
|
|
went to a site that has honeywell. here's what they got:
Aquastat
Honeywell R8182D1079 aquastat controlle R8182D1079 Y $326.04
Honeywell R8182H1070 aquastat controlle R8182H1070 Y $366.52
Control
Honeywell R8182J1042 aquastat controlle R8182J1042 Y $321.81
|

09-14-2007, 07:46 PM
|
|
|
New Member
|
|
Join Date: Sep 2007
Posts: 4
|
|
|
Thanks HZ518.
The 1079 shows all the right components to match up to my 1012. However, the 1079 does not show the 2 screws in the lower left hand corner for the CAD SULF Sensor----there are just a couple of slots there. Does one just poke the two wires from the sensor into these slots, and call it good?
Thanks,
Jesse East
|

09-14-2007, 11:37 PM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,841
|
|
|
Get two 1/4 inch spade terminals or whatever size you can determine they are and crimp them onto the Cad cell wires then insert them into the spade terminal slots.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 10,155
Threads: 6,799
Posts: 28,105
Top Poster: HayZee518 (3,841)
|
| Welcome to our newest member, mkholihan |
» Links |
|
» Online Users: 50 |
| 0 members and 50 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 02:54 AM. |
|
All times are GMT -5. The time now is 05:06 PM.