heating pipe fins?

I have hydronic hot water heating throughout the house. In some area's in various rooms, the pipes carrying the water do not have those small fins on them. Is there some kind of retro-fit kit where I can add more fins?

Thanks,
__________________
Dan
Reply With Quote
  #2 (permalink)  
Old 10-11-2007, 09:14 AM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,211
LazyPup is on a distinguished road
Adding more fins would not be a good idea.

When designing the layout of the piping system they begin by determining the BTU requirement for each room. They then design the piping in a loop or zone that will pass through two or more rooms.

The design manual lists the BTU radiation rate for finned lines. cast baseboard radiators, and the bare pipe and it gives a BTU/FT radiation value.

Just for the sake of illustration let us say the room requires 1000BTU/hr.

Now let us say the pipe has a radiation value of 20BTU/ft and the room is 20 feet long. This means the bare pipe would radiate 20bTU/ft x 20ft = 400BTU/hr.

We then deduct the 400BTU/hr for the pipe from the 1000BTU/hr required by the room and we get 1000 - 400 = 600BTU/hr.

If we were then using finned baseboard that radiates 50BTU/hr per foot we would need 600BTU/ 50BTU = 12 linear feet of finned baseboard plus the bare pipe to provide the necessary 1000BTU/HR.

If you were to arbitrarily add fins it would result in radiating too much heat in the first room on the loop, which in turn would cool the water in the line to quickly so the next room on the loop would be starved for energy.
Reply With Quote
  #3 (permalink)  
Old 10-11-2007, 09:41 AM
dkpbxman's Avatar
Handyman
 
Join Date: Nov 2005
Location: Pine Bush, NY, USA.
Posts: 94
dkpbxman
"If you were to arbitrarily add fins it would result in radiating too much heat in the first room on the loop, which in turn would cool the water in the line to quickly so the next room on the loop would be starved for energy."


Thanks, makes sense.
__________________
Dan
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,155
Threads: 6,799
Posts: 28,105
Top Poster: HayZee518 (3,841)
Welcome to our newest member, mkholihan
» Links

» Online Users: 39
0 members and 39 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 04:14 PM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0