What is the best gas line ?

Can csst ( the flexible yellow stuff ) be installed through the attic of an attached garage? Or is flexible copper piping the way to go? The gas service line is in one corner of the garage, while the ideal heater location in in the opposite corner. Any comments or suggestions would be appreciated !
Reply With Quote
  #2 (permalink)  
Old 11-18-2007, 08:58 PM
596 596 is offline
Handyman
 
Join Date: Jul 2007
Posts: 82
596 is on a distinguished road
If we are talking natural gas, some areas do not allow any copper to be used for that. Check with your local building departmentl. There was a time when you could not purchase CSST unless you had a certificate of factory training. Today, with the internet and all, it is more available. But remember, it is still gas. Leaks are bad!

If copper is OK, there should not be any mechanical joints in concealed locations. In a garage attic, that would be a matter of on-site interpretation.

And gas work always requires a permit and inspection, even where homeowners are allowed to do their own work.
Reply With Quote
  #3 (permalink)  
Old 11-19-2007, 03:25 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,841
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
I never seen copper used for gas piping. For propane soft drawn copper tubing and flare fittings yes but not for natural gas. All I've seen is black pipe and screw together fittings. In Massachusetts ALL piping is hard piped. And you need a gas license to plumb fixtures.
Reply With Quote
  #4 (permalink)  
Old 12-05-2007, 12:09 PM
New Member
 
Join Date: Dec 2007
Posts: 6
wingardclocks is on a distinguished road
In Pennsylvania you can only use any type flex connection for a very short distance. 6 feet I believe. Furthermore, Most codes that I know of requires you to use steel pipe through walls and floors. So the realality of it is, you need to run steel pipe all the way to the furnace with a shut valve at the furnace, and you will need to make a water drop also. Hope this helps.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,155
Threads: 6,799
Posts: 28,105
Top Poster: HayZee518 (3,841)
Welcome to our newest member, mkholihan
» Links

» Online Users: 46
0 members and 46 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 05:16 PM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0