Have a 20+ yr.old with a Wayne burner. Sometimes, but not all the time during start up the thermostat relay chatters (on/off-on/off-on/off etc...), then it stops and runs smoothly. Occaisionly this will occure in the middle of a cycle, but rare compaired to start up.

I justed serviced burner. Nozzle, filter, cleaned electrodes & gaped, cleane electric eye (cad), set nozzle to mixing plate distance, everthing to OME specs.

It even does it with a jumper on the T-stat terminals. Could it be the cad? How do you test these? I know it is dangerous, but can you temporarily jump the cad terminals to diagnos?
Reply With Quote
  #2 (permalink)  
Old 12-05-2007, 05:30 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,981
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
jumping the photocell won't help you because its resistance is varying and so this signal is fed to the burner relay. actually it is producing a dc voltage to the electronics of the relay. no voltage there no woikee! relay goes into lockout.
Reply With Quote
  #3 (permalink)  
Old 12-05-2007, 06:36 PM
New Member
 
Join Date: Dec 2007
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
wingardclocks is an unknown quantity at this point
So what do you suggest?
Reply With Quote
  #4 (permalink)  
Old 12-05-2007, 07:04 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,981
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
first check the heat anticipator on the thermostat. its setting should coincide with the current rating of the burner. next change the cad eye. shouldn't cost much. if your burner is a tankless hot water heater check the aquastat. it may go directly into the tank or may use a dip tube in the tank. check for loose connections on the burner relay.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,950
Threads: 7,780
Posts: 33,338
Top Poster: HayZee518 (4,981)
Welcome to our newest member, morris12
» Online Users: 40
1 members and 39 guests
randy j
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 04:46 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0