Home Repair Forum



Reply
 
LinkBack Thread Tools Display Modes
  #1 (permalink)  
Old 05-07-2008, 11:03 AM
New Member
 
Join Date: May 2008
Posts: 1
georgec is on a distinguished road
Heat pump problem (icing up)

My airconditioning system is not cooling....the unit has power, the fan runs and the compressor is operating. Howerver the condenser and coil lines are icing up when the unit is running. I replaced the filter, switched off the unit and let the ice melt, cleaned the coil fins with a garden hose (did not bend or damage the fins during this process), cleaned out any debri and trash from the outside fan. I turned the system back on and no cool air was coming from the vents (infact almost no air atr all was comong from the vent even though the fan was running. The condenser began to ice up again within 20 or 30 minutes. I am at a loss...what action should I take now?
Reply With Quote
  #2 (permalink)  
Old 05-07-2008, 11:41 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,682
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
call a hvac tech. the freon is leaking out somewhere. might be the reversing valve. users are not authorized to recharge their system unless you are epa rated and have a valid certificate for freon recovery.
Reply With Quote
  #3 (permalink)  
Old 05-07-2008, 12:33 PM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,209
LazyPup is on a distinguished road
I found this post a bit confusing. Technically speaking, in a straight cool Air Conditioner the indoor coil that is in your furnace plenum is properly called the "Evaporator Coil" and the outdoor coil that is in the compressor enclosure is called the "Condenser Coil".

By convention they are often called the same in a heat pump, although when a heat pump is in the heat mode, the function of the coils is reversed.

Whenever an evaporator coil is icing it is indicating a restricted airflow over that coil.

The most common cause of a restricted air flow are;
1. A dirty Filter, however the post states the filter has been changed.
2. Furniture or personal possessions blocking the return air grille.


Although the following problems will also cause a restricted air flow, as Hayzee has already pointed out, they would require the services of a trained HVAC technician to diagnose and service.

1.Dirty evaporator coil - requires some disassembly of the indoor unit and the coils are cleaned with a foaming chemical coil cleaning solution.

2.Low refrigerant level -Federal law requires an EPA certified refrigerant handler to check the level and/or add refrigerant as needed.

3. Defective TEV (Thermostatic Expansion Valve).

4.Defective Reversing valve (generally a reversing valve is only found on a heat pump)

5. Improper fan speed- Some heat pumps use a two speed motor which operates on high speed for AC and a lower speed for Heating. You could have a defective motor relay that has the motor stuck on the wrong speed.

6. Loose or missing sheet metal in the indoor plenum unit.

7 .Improperly adjusted room supply air register dampers. The hand operated dampers in the supply air registers are intended solely to be used to balance the air flow during initial installation and should never be changed by the homeowner.

8. A collapsed duct. This often occurs in the attic space when homeowners stack personal possessions near the ducts and the possessions later fall and collapse a duct.

Last edited by LazyPup; 05-07-2008 at 12:37 PM.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Links

» Stats
Members: 9,789
Threads: 6,636
Posts: 27,349
Top Poster: HayZee518 (3,682)
Welcome to our newest member, Mike Hansen
» Online Users: 37
1 members and 36 guests
thedcdude
Most users ever online was 388, 07-01-2007 at 01:54 AM.
» Amazon Cloud
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 05:59 PM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0