The best location of a 6 mil Vapor barrier is between the drywall and the studs or ceiling joists. that way the wood is protected too. I have heard of a special type of PAINT that can be applied in the case of no vapor barrier.
It might be worth checking this paint out as it would save you from removing ALL of your ceiling drywall in order to staple on some 6 mil poly in order to apply the vb properly.
I would think that R 40 batts in a attic floor area should be quite efficient. In my area of central Ontario, R32 (minimum) to R 40 does very well. Fiberglas batts or "blow-in" celluloise is very good.
Attic ventilation via "gravity' is all that is needed. If it's done properly, it does the job without spending many $$ on fans, wiring, electricity, etc.
SOFFIT vents and either a continuous RIDGE vent or several high, near the ridge mushroom type vents are required.
Normally, for every 300 sq ft of attic floor area, a MINIMUM of 1 sq ft of vent is required (divided 50/50 between soffit and ridge). In other words ,if the attic floor area was 40 x 30 = 1200 sq ft, you would need a MINIMUM of 4 sq ft of venting.... 2 sq ft for soffit,... 2 sq ft for ridge.
This calculation of a sq ft is based on 144 sq inches of "free" air.
Insect screens are very restrictive, so in order to have a free area of 1 sq. ft., the vent may have to be approx 50 % larger depending on the size of the screens restriction)