hot water heating drip

hello, over the summer i extended a porch into the backyard and added additional baseboard heating. when the heat is on now there is a constant drip from overpress valve. i allready replaced expansion tank to no avail.i wonder if a new valve with higher btu rating may help. thank you for info
Reply With Quote
  #2 (permalink)  
Old 01-10-2004, 11:54 AM
New Member
 
Join Date: Jan 2004
Location: .
Posts: 17
Joel
It;s not to do with btu,s its a presser valve and should read around 12 to 15 psi if it;s higher release some water from the boiler (should be a valve on the bottom)if the psi is correct and it leaks it needs replacing this is a common problem and easy to replace'shut off boiler close water vales feeding boiler replace valve turn on water ,fire boiler adjust pressure (p.s.valve max;s at 30 psiand releases after that its a safty)shut off boiler after reachs temp. and pressure and bleed rads highest in the house turn on boiler
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,155
Threads: 6,799
Posts: 28,105
Top Poster: HayZee518 (3,841)
Welcome to our newest member, mkholihan
» Links

» Online Users: 56
0 members and 56 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 05:03 PM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0