Payne Furnace Blower Motor Problem

I am a new member of this forum and am hoping that some of you cleaver people out there can help me with my problem.

I have a 1990 vintage Payne series A forced air furnace with two problems both associated with the blower motor.

The first is when the blower motor is first switched on. The motor starts to turn but does not quite reach speed and goes off for a few seconds. The motor then switches back on and the second time it spins up to speed just fine.

I took the blower motor out, cleaned and oiled the bronze bearings and also replaced the filter and this seems to have improved things. I was wondering if replacing the run capacitor would be worth a try?

The second problem is at the other end of the furnace cycle when the blower turns off. The motor stops turning for a few seconds, comes back on for 2-3 seconds, and repeats this cycle 2-3 times.

After looking at the (partial) diagram on the inside of the furnace and searching this forum, I wondered if the plenum T/stat was the likely cause of this problem? (The sensor is a STEMCO 430-1457 HH12ZA174c).

Any suggestions welcome.

Thanks!
Reply With Quote
  #2 (permalink)  
Old 01-03-2009, 07:22 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,918
Thanks: 0
Thanked 97 Times in 97 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
take the motor apart again and clean off the centrifugal switch contacts. use a piece of 400 grit sandpaper NOT emery cloth. make sure the flyball weights are free to move outward. look at the nylon rubbing block on the flyball make sure it isn't grooved. what this does is disconnect the start capacitor when the motor is up to running speed. when you re-assemble the motor if there are any fiber spacers, make sure you got the proper number on either or both sides. these help keep the rotor centered in the magnetic field. a little bit of slide slop is ok. the plenum stat is a hi limit and run limit. if the proportional band is too close then the switch will be telling the motor to operate.
Reply With Quote
  #3 (permalink)  
Old 01-03-2009, 08:26 PM
New Member
 
Join Date: Jan 2009
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
markshew is an unknown quantity at this point
First of all, thank you so much for the prompt reply!

I had no idea that there was a centrifugal switch within the motor itself so I will have another go at that as you suggested.

I should have also mentioned that I added an in-line booster fan to help circulate the air to the upper level of the house. I took the power for the additional fan straight off the control PCB using "piggy back" spade connectors where the main blower motor gets it's feed. The start problem seems to be less prevelent if I switch off the booster fan (I added a rheostat to control the booster fan speed). I wondered if this was part of the problem by wearing out the relay contacts prematurely due to the additional load?

Regarding the plenum stat. There is no adjustment that I can see on the unit so do you suggest replacing it?

Also, when I looked at it again today, I found that there are actually what appear to be another stat / sensor in series with it, with the 2nd one being a TO3 metal can configuration mounted on a part of the furnace where air is drawn in and mixed with the combusted gas. Both the plenum T/Stat and this second sensor appear to be "normally closed" when measured with an Ohm meter with the furnace off.
Reply With Quote
  #4 (permalink)  
Old 01-03-2009, 11:54 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,918
Thanks: 0
Thanked 97 Times in 97 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
a rheostat is fine where you control the speed of a dc motor but I wouldn't suggest it in an ac motor. for that a tapped autotransformer works best but these tend to be pricey. I got one for my bench testing that goes from zero to 130 volts ac. cost about $50. the can type "stat" is a klixon overload that uses a bi-metal switch. when it heats up it opens, when it cools down it closes.
Reply With Quote
  #5 (permalink)  
Old 01-04-2009, 08:11 PM
New Member
 
Join Date: Jan 2009
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
markshew is an unknown quantity at this point
Again, thanks for the prompt reply!

After your advise about not using a rheostat to control the booster fan speed, I went to remove it and discovered that it is actually a fan speed controller made by Leviton {6616-1XL). After checking the spec sheet it seems to be OK for the application but I would appreciate your input.

BTW, do you expect that the cleaning of the centrifugal contacts will help with the starting or the stopping problem?

What I thought was the plenum stat looks to be an overtemperature sensor in the heat exchanger as the gas supply is cut off when it is disconnected. I will have to look elsewhere for the plenum stat.
Reply With Quote
  #6 (permalink)  
Old 01-11-2009, 12:07 AM
New Member
 
Join Date: Jan 2009
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
markshew is an unknown quantity at this point
Well, I took the motor apart as suggested and low and behold, no centrifugal switch contacts at all! There was nothing inside the motor apart from the stator and windings so now I at a loss as to what to do next. The only thing that I can think of doing is to change out the run capacitor.

Failing that, I may have to admit defeat and call in the repair man.

Any other suggestions anyone?
Reply With Quote
  #7 (permalink)  
Old 01-11-2009, 01:26 AM
Handyman
 
Join Date: Feb 2008
Location: Evansville, In
Posts: 167
Thanks: 2
Thanked 16 Times in 16 Posts
jnaas2 is an unknown quantity at this point
Send a message via AIM to jnaas2
The capicator you are talking about if its a start capicator it will be light if you remove it, if its a run capicator it will be filled with oil and be heavy for its size, it shoud say somewhere what it is. The one thing that will cause a fan to turn off and on is the fan control its a sguare looking box that also is the high temperature limit and if you take the cover off it will have a circular dial with temperature readings on it. If your furnance is circuit board controled it may be going out. If you can send a wiring diagram it will be easier to answer your question
Reply With Quote
  #8 (permalink)  
Old 01-11-2009, 12:28 PM
hvacwiz's Avatar
Handyman
 
Join Date: Apr 2006
Location: Ohio
Posts: 80
Thanks: 0
Thanked 6 Times in 6 Posts
hvacwiz is an unknown quantity at this point
I would suggest instead of spending all your time screwing around with it, to shell out 80-100 bucks for a new motor and be done with it.
Reply With Quote
  #9 (permalink)  
Old 01-11-2009, 01:19 PM
New Member
 
Join Date: Jan 2009
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
markshew is an unknown quantity at this point
Jnaas2

Thanks for the suggestion.

I have absolutely no problem buying a new motor but I would like to understand why it is that you think that the symptoms I describe are due to a bad motor?

I am an engineer and really dislike just changing parts out and not understanding the problem.

Thanks,
Reply With Quote
  #10 (permalink)  
Old 01-11-2009, 10:53 PM
Handyman
 
Join Date: Feb 2008
Location: Evansville, In
Posts: 167
Thanks: 2
Thanked 16 Times in 16 Posts
jnaas2 is an unknown quantity at this point
Send a message via AIM to jnaas2
Markshew
Im like you I have a lot of fun trying to figure out why something doesnt work, and PATTING Myself on the back when I get it right the first time. Im not a engineer but I hold a Master electrician license, Master plumbing license and a Commercial and Residential contractors licenses. Lets us know what you find out
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,842
Threads: 7,748
Posts: 33,125
Top Poster: HayZee518 (4,918)
Welcome to our newest member, nerbonne
» Online Users: 48
0 members and 48 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 06:55 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0