  #1 (permalink)  
Old 01-15-2009, 12:24 PM
New Member
 
Join Date: Jan 2009
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
bmik2729 is an unknown quantity at this point
Trane XE78

I have the above mentioned furnace and it has been acting up recently. It is @ 16 years old. Every once in a while (more frequently each day) the furnace turns on but blows only cold air. I opened it up and cleaned up around the venturis, the ignitor and the flame sensor, etc.
Basically the unit cycles up normally, the inductor fan comes on, then the ignitor glows very brightly but the gas never ignites. Then the ignitor goes out but the air fan turns on and obviously blows only cold air.
Usually when this happens if I simply power off at the main switch, wait a minute and turn it back on it works okay for a few hours. I put a new Honeywell thermostat on last summer that tries to keep the temp within 1 degree. The furnace is turning on a lot...sometimes within a minute of shutting off. Is it just cycling too much or is something else to blame?
Reply With Quote
  #2 (permalink)  
Old 01-15-2009, 01:24 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
You set the heat anticipator according to the current draw marked on the gas valve. This adjusts the cycling of the furnace.
Reply With Quote
  #3 (permalink)  
Old 01-15-2009, 01:43 PM
New Member
 
Join Date: Jan 2009
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
bmik2729 is an unknown quantity at this point
The cycling is a thermostat problem that did not exist with my original thermostat which had a 'swing' setting (or differential setting) set at 3 degrees. The Honeywell is permanently set at 1 degree...much too tight.
The real problem is the failure to ignite. It almost appears as though no fuel is being supplied.
Reply With Quote
  #4 (permalink)  
Old 01-16-2009, 05:31 AM
New Member
 
Join Date: Jan 2009
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
bmik2729 is an unknown quantity at this point
Still fails

I replaced he thermostat to one with a 2.25 degree swing setting and the seeming constant cycling of the unit has stopped. The temp must now drop more then 2 degrees before the heat will come on. I also discovered that the inducer motor was loose and was making a lot of noise and vibrating. I read somewhere that excess vibration could cause the pressure switch to not read properly. I tightened it back up and the unit is much quieter now and vibrates less. All worked flawlessly for almost 12 hours and then it failed to ignite again. All it needed to fire up was to shut the unit down at the main switch, wait 30 seconds (less) and power back on and it fired up as normal. It appears I am going to have to start replacing components. It is a Trane TUD080C936A1 with a WHite-Rogers 50A50-405 controller. Any suggestions are appreciated.

Last edited by bmik2729; 01-16-2009 at 05:44 AM..
Reply With Quote
  #5 (permalink)  
Old 01-17-2009, 01:42 PM
New Member
 
Join Date: Jan 2009
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
bmik2729 is an unknown quantity at this point
bumping up

It ran for 24 hours before it failed to ignite again. This time though I was able to get the controller status: 2 flashes = System Lockout. I think I am going to jumper the air pressure switch closed to eliminate it as the culprit. The inducer blower motor is turning...is it possible that on occasion it is not creating enough airflow and it could be the problem?
Reply With Quote
  #6 (permalink)  
Old 01-17-2009, 04:25 PM
Handyman
 
Join Date: Feb 2008
Location: Evansville, In
Posts: 167
Thanks: 2
Thanked 16 Times in 16 Posts
jnaas2 is an unknown quantity at this point
Send a message via AIM to jnaas2
Ive seen the impellor blades come off the inducer moto shaft and the motor would run but not the blades. And I found a single tree leaf that made it all the way to the furnance intake screen and wouldnt allow the inducer motor to pull enough of a vacume.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,943
Threads: 7,776
Posts: 33,324
Top Poster: HayZee518 (4,977)
Welcome to our newest member, GLE3
» Online Users: 48
1 members and 47 guests
paul52446m
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 08:07 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0