Baseboard hot water heat - gurgling noise in piping

I am hoping someone can explain the following situation.

My home has baseboard hot water heating using an oil fired furnace. The water piping is a closed loop system. There is an inlet valve for make-up water, but the valve is closed. There is an expansion tank on the outlet water pipe from the furnace, and the air pressure in the tank is at 12 psi (I checked). There is an air purge on the outlet water pipe from the furnace, and it does work because I do on occasion hear air escaping from the purge valve.

Occasionally I hear gurgling in the water piping in the house. I assume that the gurgling noise is due to air pockets in the water. The furnace is 4 years old and I have seen no water leaks that might allow air to enter the system. I never have to add make-up water to maintain the water pressure. I have seen no water leaks from the system. I assume that if water was leaking, the water pressure would decrease over time.

What is interesting is that the gurgling is noise is heard only every few days. Strange!!

If I have an air purge, I would think that the air would eventually be purged and I would no longer hear the gurgling. And since the water piping is a closed loop system, no air can enter the piping. I would think that eventually all of the air would be purged and I would no longer hear the gurgling. So why does the gurgling continue year after year? What am I not understanding?
Reply With Quote
  #2 (permalink)  
Old 02-17-2009, 01:31 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
water when heated will dissolve out oxygen and hydrogen out of liquid over time. it is this mixture that you hear gurgling through the pipes. the gas seeks to find the highest level in the system and it's HERE that it should be vented.
Reply With Quote
  #3 (permalink)  
Old 02-18-2009, 03:45 AM
Redwood's Avatar
Handyman
 
Join Date: Feb 2009
Location: Connecticut
Posts: 159
Thanks: 10
Thanked 15 Times in 14 Posts
Redwood will become famous soon enough
Some systems do not have bleeders at the high point.
On these a hose is placed on a drain by the boiler, with the circulator off, certain valves closed, and fill water is run through the system to force the air out the hose because of the high flow rate. It is probably best if you could have someone that knows what they are doing show you how to do it if you don't have bleeders.

Last edited by Redwood; 02-18-2009 at 03:49 AM..
Reply With Quote
  #4 (permalink)  
Old 02-19-2009, 02:26 PM
New Member
 
Join Date: Apr 2008
Location: Maryland
Posts: 15
Thanks: 0
Thanked 0 Times in 0 Posts
jdc0222 is an unknown quantity at this point
I think the inlet valve should be kept open. That will replace any water that vaporizes and escapes through the purge valve.
Reply With Quote
  #5 (permalink)  
Old 03-02-2009, 03:26 AM
Redwood's Avatar
Handyman
 
Join Date: Feb 2009
Location: Connecticut
Posts: 159
Thanks: 10
Thanked 15 Times in 14 Posts
Redwood will become famous soon enough
Quote:
Originally Posted by jdc0222 View Post
I think the inlet valve should be kept open. That will replace any water that vaporizes and escapes through the purge valve.
That would be correct!
Good catch!
__________________
I stayed at a Holiday Inn Express last night.
Now I can Plumb!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


For great information on the history of sanitary sewers including the use of Redwood Pipe
Visit
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Did you know some Redwood Pipe is still in service today.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,943
Threads: 7,776
Posts: 33,325
Top Poster: HayZee518 (4,977)
Welcome to our newest member, GLE3
» Online Users: 41
1 members and 40 guests
radstorm
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 10:06 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0