Oil Burner fails to ignite
I have a Beckett burner using a transformer along with a stack relay on the flue. Occassionally the burner will fail to ignite. It will not even attempt to start. I have to ajust the springs on the eclectrodes in order to get it to ignite. At times when the furnace is idle I will move the aquastat to a higher temp and the burner does not even attempt to start. At this point I hit the reset on the Stack
relay and the burner starts but fails to ignite at the transformer. I then readjust the springs on the transformer and hit the reset and the
burner starts ignition and all. This will run with no problems for a day or two then the same thing happens. Any idea's
Hune you out there
|

01-21-2004, 07:29 AM
|
|
Journeyman
|
|
Join Date: Nov 2003
Location: .
Posts: 445
Thanks: 0
Thanked 0 Times in 0 Posts
|
|
|
Welcome to the forum.... If your having to re-adjust the electrodes from time to time, this is ONE of the problems. Also the settings (gap ) is very critical in the firing of the burner. Nozzle sizing, spray pattern ,should also be set properly. UNLESS you have the required testers and "settings" manual,Air/fuel ratio, etc, all your going to accomplish is creating a safety hazard. When you have to re-set the stack relay (lock-out)that is shutting the system down for your protection. In the long run, having a PRO come in and make any necessary adjustments would be the best advice at this time. Good luck, Hube
|

01-23-2004, 04:02 PM
|
|
New Member
|
|
Join Date: Jan 2004
Location: Huntington, NY, USA.
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
|
|
|
Great reply there Hube,,,,I have changed the electrodes, they are gapped properly.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 12,943
Threads: 7,777
Posts: 33,326
Top Poster: HayZee518 (4,977)
|
| Welcome to our newest member, GLE3 |
» Links |
|
» Sponsors |
|
|
|
All times are GMT -5. The time now is 10:56 PM.