nortron furnace migraine

hello...i have a 4 year old(give or take) electric 25 kw nortron furnace....the fan drops to low when the t-stat tells it to shut off and it stays on forever...only way to shut it off is with main breaker...no switches were tripped or touched..everything worked fine all 4 years so it`s not a bad wiring job issue...the fan alone,no heat, decided to stay on a few weeks ago....there are three switches on furnace itself...summer switch is set to heating.....energy saver switch is set to cold weather..... fan control switch is set to automatic....there`s also a green light on the furnace which says t-stat on....t-stat controls are set to heat and auto....these switches have been like this all winter.....now fan won`t shut off..there is also an air conditioner hooked up to this unit....25KW, 240 Volt D Series Electric Furnace
Model 21D25....no model # written on furnace...not positive on model #....how do i trouble-shoot this problem so i can buy whatever part i need????which wires do i pull to test this and that?????please help....
Reply With Quote
  #2 (permalink)  
Old 05-20-2009, 08:16 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
the fan I'm guessing operates off a fan contactor or fan relay. there is an operating coil that keeps the contacts closed. if the operating coil got fried while the contacts were closed, mechanically they'd stay closed. the contacts could have welded together closed. if when you shut off the breaker for the fan you notice the contacts did not open then suspect welded contacts.
Reply With Quote
  #3 (permalink)  
Old 05-21-2009, 09:44 AM
New Member
 
Join Date: May 2009
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
luc12 is on a distinguished road
norton furnace migraine

thanks for replying; I`ve attached a picture of the wiring so you can have a better idea of what`s what..hope it works....never done this before......I went to the furnace and my wife was turning breaker on and off and there was no clicking sound or nothing when the fan was turning on and off.....don`t see any contacts;just relays..i think the big red wire on the bottom right is the low power for the fan...i could pull that but then the motor would go straight to high ...probably not good....any help? thanks
Attached Images
File Type: jpg furnace 003.jpg (63.8 KB, 4 views)
Reply With Quote
  #4 (permalink)  
Old 05-21-2009, 12:45 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
I made a copy of your picture. I'll get it into "paint" and make some annotations as to what is there and re-post it later today
Reply With Quote
  #5 (permalink)  
Old 05-21-2009, 01:05 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
Electric furnace

The larger area are your heat elements. the whitish circles are the element overloads. these are wired normally closed. the wires grouped together are the common(s) to all heater elements and go to one terminal on the main bus. The sequencers are wired into a control circuit somewhere else. as more heat is needed a sequencer will turn on and in turn turn on an element. look to the diagram under all the wires. it'll give you some idea of how this panel is wired.
Attached Images
File Type: jpg furnace 003.jpg (67.8 KB, 2 views)
Reply With Quote
  #6 (permalink)  
Old 05-21-2009, 07:16 PM
New Member
 
Join Date: May 2009
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
luc12 is on a distinguished road
OK; my best guess is the 240 volt relay...bottom right...the only reason is that the low speed red wire comes off of this to the fan motor....i know nothing about furnaces....that`s why i ask the people who do..that being said,what do you think?.....thanks for your help....
Reply With Quote
  #7 (permalink)  
Old 05-21-2009, 07:38 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
That being the case replace the relay.
Reply With Quote
  #8 (permalink)  
Old 05-21-2009, 08:31 PM
New Member
 
Join Date: May 2009
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
luc12 is on a distinguished road
so you agree it`s the relay?
Reply With Quote
  #9 (permalink)  
Old 05-21-2009, 08:58 PM
New Member
 
Join Date: May 2009
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
luc12 is on a distinguished road
update.....i went back to the furnace with breaker on and the t-stat set to off...fan was running on low...i pulled the red fan wire and fan shut off and i saw the closest element start glowing red....that now explains the fan being on...i didn`t notice the element was on before because with the fan running,the element doesn`t glow as much...now my question is why is that element on with the t-stat set to off?thanks in advance,anyone?
Reply With Quote
  #10 (permalink)  
Old 05-21-2009, 09:22 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
can you make a copy of the schematic diagram and somehow get it to me?
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,943
Threads: 7,776
Posts: 33,324
Top Poster: HayZee518 (4,977)
Welcome to our newest member, GLE3
» Online Users: 36
2 members and 34 guests
jnaas2, paul52446m
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 08:31 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0