HELP!! HVAC Problem
My HVAC will not cool the home. Home warranty company doesn't know what the issue is. Home warranty tech says ac is good and working fine. He temped the the return air which measured 62 degrees the supply in the attic measured 65 to 68 and out of the vents he says it measured 72-79 depending upon room and duct length to that room.
Replaced evaporator coil about a year ago. Had an independent contractor inspect ac who believes it is compressor, compressor was leaking oil, and he believes valves bad he also checked ducts and said they were fine.
At a loss as to what problem truly is. Warranty company says they won't replace compressor and keeps saying its probably a duct problem but not sure. Any help advice or diagnosis would be appreciated!
|

06-08-2009, 03:32 PM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 5,643
Thanks: 0
Thanked 180 Times in 175 Posts
|
|
|
oil just doesn't evaporate, look for spots or a coating on any piping in the area of the compressor. leaking oil will compromise your compressor and anything inside that moves and is lubricated. freon will leak out along with the oil. valves can be reed type or valves like in a car if the system is big enough. reed valves use a tempered spring steel sheet with a spring plate behind it. have your tech put gauges on the system and measure high side and low side pressures. a high gauge that oscillates indicates a leak.
|

06-08-2009, 08:12 PM
|
|
 |
Contractor
|
|
Join Date: Mar 2006
Location: North Carolina
Posts: 1,069
Thanks: 0
Thanked 75 Times in 72 Posts
|
|
Quote:
Originally Posted by mlincoln
He temped the the return air which measured 62 degrees the supply in the attic measured 65 to 68 and out of the vents he says it measured 72-79 depending upon room and duct length to that room.
|
65-68 in the attic and 72-79 at the register ?????......that's a huge swing, these ducts in the attic are they insulated, there shouldn't be a swing of anywhere near 10 F from duct to register.
__________________
|
|
The Following User Says Thank You to pushkins For This Useful Post:
|
|

06-08-2009, 10:50 PM
|
|
Handyman
|
|
Join Date: Feb 2008
Location: Evansville, In
Posts: 177
Thanks: 2
Thanked 17 Times in 17 Posts
|
|
|
You say the return air measured 62 and that the supplys measured 72-79 are you sure your not stating this backwards. Normally when you are in the a/c mode the supply air measures 15 - 20 degrees colder then the return air ?. You didnt state if you have gas or electric I have seen a sequencer stick and the air conditioning and part of the heat operate at the same time
|
|
The Following User Says Thank You to jnaas2 For This Useful Post:
|
|

06-09-2009, 05:25 PM
|
|
New Member
|
|
Join Date: Jun 2009
Posts: 13
Thanks: 5
Thanked 0 Times in 0 Posts
|
|
|
thanks
I did have it backwards. Thanks to all of your comments. The warranty place is going to replace the compressor as they found that that is the problem. Your comments help educate me as to what to ask them.
|

06-09-2009, 07:32 PM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 5,643
Thanks: 0
Thanked 180 Times in 175 Posts
|
|
|
the refrigeration system in an air conditioner or a refrigerator is essentially the same. you are taking a hot atmosphere and through the freon are exchanging hot for cool.
|

06-17-2009, 02:20 PM
|
|
New Member
|
|
Join Date: Jun 2009
Posts: 13
Thanks: 5
Thanked 0 Times in 0 Posts
|
|
|
Ok the problem still persists
AHHHHH! Ok New compressor installed and still the house isn't cooling. The Air from the AC is good and cool? However when it enters the duct to the supply in the home it heats up on average about 10-15 degrees. Everyone who has inspected the duct (3 different people so far) says that the insulation around the duct is good and that there are no kinks or holes in the ducts. They have commented however on how strange it is for the air to heat up so rapidly. When the air exits into the house through the vents its about 10-15 degrees higher. What can the problem be? Since we have been trouble shooting for the last two weeks we found out the AC unit is ok and the ducts have no visible wear nor is the insulation torn or worn. We are left with either clogged or dirty ducts or possibly the attic fans not working properly or possibly the need of new attic fans/vents to cool the attic? Any other suggestions or diagnosis regarding this problem? Your comments and or suggestions are greatly appreciated and welcomed.
|

06-17-2009, 02:38 PM
|
|
 |
Handyman
|
|
Join Date: Sep 2006
Location: IL
Posts: 168
Thanks: 3
Thanked 2 Times in 2 Posts
|
|
|
what is the supply air temp RIGHT at the air handler? 55 or so I hope
__________________
Is it beer thirty??
|

06-17-2009, 02:48 PM
|
|
New Member
|
|
Join Date: Jun 2009
Posts: 13
Thanks: 5
Thanked 0 Times in 0 Posts
|
|
|
it read 60 degrees according to warranty tech
|

06-18-2009, 06:42 AM
|
|
 |
Contractor
|
|
Join Date: Mar 2006
Location: North Carolina
Posts: 1,069
Thanks: 0
Thanked 75 Times in 72 Posts
|
|
|
If the air entering the ducts is 55 - 60 and while in the ducts in the attic it increases 10-15 degrees, then the problem obviously exists in the attic area.
Given that I doubt that anyone installed a heater inside the ductwork (lol....although that would make for a good hidden camera show) and conditioned air doesn't change 10-15 degrees that quickly up or down without a great deal of help I'd be looking at the attic temps. Ducting run in attics has always created a problem due to sometimes very hot attics with poor ventilation.
What is the temp. of your attic ?
At what temp. are your vents turning on ? (check the fans thermostat)
Is there a good flow of air coming out of all the vents serviced from the attic ?
__________________
|
 |
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 14,576
Threads: 8,534
Posts: 37,184
Top Poster: HayZee518 (5,643)
|
| Welcome to our newest member, window |
» Online Users: 31 |
| 0 members and 31 guests |
| No Members online |
| Most users ever online was 400, 06-22-2009 at 06:11 AM. |
» Links |
|
» Sponsors |
|
|
|
All times are GMT -5. The time now is 05:42 AM.