HELP!! HVAC Problem

My HVAC will not cool the home. Home warranty company doesn't know what the issue is. Home warranty tech says ac is good and working fine. He temped the the return air which measured 62 degrees the supply in the attic measured 65 to 68 and out of the vents he says it measured 72-79 depending upon room and duct length to that room.

Replaced evaporator coil about a year ago. Had an independent contractor inspect ac who believes it is compressor, compressor was leaking oil, and he believes valves bad he also checked ducts and said they were fine.

At a loss as to what problem truly is. Warranty company says they won't replace compressor and keeps saying its probably a duct problem but not sure. Any help advice or diagnosis would be appreciated!
Reply With Quote
  #2 (permalink)  
Old 06-08-2009, 04:32 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,918
Thanks: 0
Thanked 97 Times in 97 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
oil just doesn't evaporate, look for spots or a coating on any piping in the area of the compressor. leaking oil will compromise your compressor and anything inside that moves and is lubricated. freon will leak out along with the oil. valves can be reed type or valves like in a car if the system is big enough. reed valves use a tempered spring steel sheet with a spring plate behind it. have your tech put gauges on the system and measure high side and low side pressures. a high gauge that oscillates indicates a leak.
Reply With Quote
  #3 (permalink)  
Old 06-08-2009, 09:12 PM
pushkins's Avatar
Contractor
 
Join Date: Mar 2006
Location: North Carolina
Posts: 740
Thanks: 0
Thanked 31 Times in 29 Posts
pushkins will become famous soon enough
Quote:
Originally Posted by mlincoln View Post
He temped the the return air which measured 62 degrees the supply in the attic measured 65 to 68 and out of the vents he says it measured 72-79 depending upon room and duct length to that room.
65-68 in the attic and 72-79 at the register ?????......that's a huge swing, these ducts in the attic are they insulated, there shouldn't be a swing of anywhere near 10 F from duct to register.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote
The Following User Says Thank You to pushkins For This Useful Post:
mlincoln (06-17-2009)
  #4 (permalink)  
Old 06-08-2009, 11:50 PM
Handyman
 
Join Date: Feb 2008
Location: Evansville, In
Posts: 167
Thanks: 2
Thanked 16 Times in 16 Posts
jnaas2 is an unknown quantity at this point
Send a message via AIM to jnaas2
You say the return air measured 62 and that the supplys measured 72-79 are you sure your not stating this backwards. Normally when you are in the a/c mode the supply air measures 15 - 20 degrees colder then the return air ?. You didnt state if you have gas or electric I have seen a sequencer stick and the air conditioning and part of the heat operate at the same time
Reply With Quote
The Following User Says Thank You to jnaas2 For This Useful Post:
mlincoln (06-17-2009)
  #5 (permalink)  
Old 06-09-2009, 06:25 PM
New Member
 
Join Date: Jun 2009
Posts: 13
Thanks: 5
Thanked 0 Times in 0 Posts
mlincoln is on a distinguished road
thanks

I did have it backwards. Thanks to all of your comments. The warranty place is going to replace the compressor as they found that that is the problem. Your comments help educate me as to what to ask them.
Reply With Quote
  #6 (permalink)  
Old 06-09-2009, 08:32 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,918
Thanks: 0
Thanked 97 Times in 97 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
the refrigeration system in an air conditioner or a refrigerator is essentially the same. you are taking a hot atmosphere and through the freon are exchanging hot for cool.
Reply With Quote
  #7 (permalink)  
Old 06-17-2009, 03:20 PM
New Member
 
Join Date: Jun 2009
Posts: 13
Thanks: 5
Thanked 0 Times in 0 Posts
mlincoln is on a distinguished road
Ok the problem still persists

AHHHHH! Ok New compressor installed and still the house isn't cooling. The Air from the AC is good and cool? However when it enters the duct to the supply in the home it heats up on average about 10-15 degrees. Everyone who has inspected the duct (3 different people so far) says that the insulation around the duct is good and that there are no kinks or holes in the ducts. They have commented however on how strange it is for the air to heat up so rapidly. When the air exits into the house through the vents its about 10-15 degrees higher. What can the problem be? Since we have been trouble shooting for the last two weeks we found out the AC unit is ok and the ducts have no visible wear nor is the insulation torn or worn. We are left with either clogged or dirty ducts or possibly the attic fans not working properly or possibly the need of new attic fans/vents to cool the attic? Any other suggestions or diagnosis regarding this problem? Your comments and or suggestions are greatly appreciated and welcomed.
Reply With Quote
  #8 (permalink)  
Old 06-17-2009, 03:38 PM
Java_Bob's Avatar
Handyman
 
Join Date: Sep 2006
Location: IL
Posts: 150
Thanks: 2
Thanked 2 Times in 2 Posts
Java_Bob is an unknown quantity at this point
what is the supply air temp RIGHT at the air handler? 55 or so I hope
__________________
Is it beer thirty??
Reply With Quote
  #9 (permalink)  
Old 06-17-2009, 03:48 PM
New Member
 
Join Date: Jun 2009
Posts: 13
Thanks: 5
Thanked 0 Times in 0 Posts
mlincoln is on a distinguished road
it read 60 degrees according to warranty tech
Reply With Quote
  #10 (permalink)  
Old 06-18-2009, 07:42 AM
pushkins's Avatar
Contractor
 
Join Date: Mar 2006
Location: North Carolina
Posts: 740
Thanks: 0
Thanked 31 Times in 29 Posts
pushkins will become famous soon enough
If the air entering the ducts is 55 - 60 and while in the ducts in the attic it increases 10-15 degrees, then the problem obviously exists in the attic area.
Given that I doubt that anyone installed a heater inside the ductwork (lol....although that would make for a good hidden camera show) and conditioned air doesn't change 10-15 degrees that quickly up or down without a great deal of help I'd be looking at the attic temps. Ducting run in attics has always created a problem due to sometimes very hot attics with poor ventilation.
What is the temp. of your attic ?
At what temp. are your vents turning on ? (check the fans thermostat)
Is there a good flow of air coming out of all the vents serviced from the attic ?
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,842
Threads: 7,748
Posts: 33,125
Top Poster: HayZee518 (4,918)
Welcome to our newest member, nerbonne
» Online Users: 47
0 members and 47 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 06:54 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0