Indoor Fan HVAC

Today I tried to turn on my central air and the trane new unit as of 2 years is on outside however the indoor fan won't kick on. There is condensation on the wiring near the iniside wiring meaning the cool air is trying to get through but the fan won't blow it into the house. It had tripped a breaker off the main in the house, when i repaired that it still didn't kick on..why might the fan not be kicking on? Any suggestions welcome maybe some tennis tickets to the best quick response!!!
Reply With Quote
  #2 (permalink)  
Old 07-27-2009, 08:42 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,978
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
reset the circuit breaker and see what happens. the fan, if its not too large a unit will come off a fan relay. if its a large unit then look for an tripped overlaod on a fan contactor. a relay or a contactor's purpose is to switch a high current load using a lower voltage coil. the fan will operate off a thermostat circuit of 24 volts
Reply With Quote
The Following User Says Thank You to HayZee518 For This Useful Post:
Tennis Fan (07-27-2009)
  #3 (permalink)  
Old 07-27-2009, 09:24 PM
New Member
 
Join Date: Jul 2009
Posts: 2
Thanks: 1
Thanked 0 Times in 0 Posts
Tennis Fan is on a distinguished road
Where in the house would I find the tripped overload on the fan contractor?
Reply With Quote
  #4 (permalink)  
Old 07-27-2009, 11:01 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,978
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
look in the control panel for the a/c. it'll be a seperate cabinet adjacent to the furnace.
Reply With Quote
  #5 (permalink)  
Old 07-30-2009, 02:44 AM
HandymanTrainer's Avatar
New Member
 
Join Date: Jul 2009
Location: Marana, AZ
Posts: 22
Thanks: 1
Thanked 3 Times in 3 Posts
HandymanTrainer is on a distinguished road
Two year old trane, eh? I would see if you can jumper the fan black wire to a primary hot wire. If the fan works when run direct to power, the most likely cause of the problem is your control board. If two year old or less it should still be under warranty.

HandymanTrainer
__________________
http://www.thefixitteacher.com
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,946
Threads: 7,778
Posts: 33,327
Top Poster: HayZee518 (4,978)
Welcome to our newest member, mitchell123
» Online Users: 33
0 members and 33 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 08:57 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0