ok, you've checked and cleaned the trap ,lines,everything below the entrance to the trap.Make sure the vent pipe is not creating this condensate and leaking into the exchanger. (this would be rare) The problem being still there, tells me there is an obstruction above, such as a "off-level" condensate pan or a damaged base to this entry pan. You will have to remove the blower assembly to get at it. Keep us posted, and good luck, Hube
|