HVAC fan intermittent

My blower fan is intermittent, and this occurs during both heating and cooling demand.

For example, I am currently running air conditioning and the blower fan will kick out for about 1 to 2 minutes, even though the thermostat continues to call for cooling and the condenser unit continues to run (fan on the condenser unit is spinning). Then the blower fan will come back on and run normally for anywhere from a few minutes to a few hours, and then the problem will occur again.

When the blower fan kicks out, it will not turn on even when I switch the fan switch on the thermostat to the "continuous run" position.

Is this most likely a fan relay problem, a motor problem, or a control module problem? Any suggestion on how to troubleshoot?

The unit is a Rheem propane forced air furnace with a Lennox air conditioner added about 5 year ago.

Thanks!
Reply With Quote
  #2 (permalink)  
Old 08-26-2009, 05:25 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,978
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
probably is a fan relay because this seems to be super imposed between the thermostat and the motor. if you could post a schematic of your unit, this would help us troubleshoot your problem, otherwise its a shot in the dark what the problem might be.
Reply With Quote
The Following User Says Thank You to HayZee518 For This Useful Post:
herbertjd13 (08-26-2009)
  #3 (permalink)  
Old 08-26-2009, 10:17 AM
New Member
 
Join Date: Aug 2009
Posts: 8
Thanks: 2
Thanked 0 Times in 0 Posts
herbertjd13 is on a distinguished road
Many thanks for your input.

A schematic is attached.
Attached Images
File Type: jpg scan0006.jpg (18.0 KB, 4 views)
Reply With Quote
  #4 (permalink)  
Old 08-26-2009, 10:33 AM
New Member
 
Join Date: Aug 2009
Posts: 8
Thanks: 2
Thanked 0 Times in 0 Posts
herbertjd13 is on a distinguished road
Noticed the schematic is not readable; will see what I can do to make it larger.
Reply With Quote
  #5 (permalink)  
Old 08-26-2009, 10:47 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,978
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
yeah, I just looked at it. my zoom makes it worse.
Reply With Quote
  #6 (permalink)  
Old 08-26-2009, 10:56 AM
New Member
 
Join Date: Aug 2009
Posts: 8
Thanks: 2
Thanked 0 Times in 0 Posts
herbertjd13 is on a distinguished road
Thanks again. Here's a .pdf that's not great, but much better.
Attached Files
File Type: pdf scan0002.pdf (17.8 KB, 3 views)
Reply With Quote
  #7 (permalink)  
Old 08-26-2009, 11:09 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,978
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
ok print shows a door interlock switch, on the left part of the ladder diagram, next is a fan control [looks like a thermal device] [normally open] then a system relay normally open that goes to the exhaust blower.
if you can open the chat in here - look up top on the forum page for CHAT go in there.
Reply With Quote
  #8 (permalink)  
Old 08-26-2009, 11:45 AM
New Member
 
Join Date: Aug 2009
Posts: 8
Thanks: 2
Thanked 0 Times in 0 Posts
herbertjd13 is on a distinguished road
Sorry I missed you. Unfortunately, will be out now until late afternoon/early evening (I'm in Colorado).

It also said I had a private message but could not open that as it was blocked initially and then I coudn't find it again.
Reply With Quote
  #9 (permalink)  
Old 08-26-2009, 12:01 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,978
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
Furnace

Re-drawn diagram
Print shows 5 & 6 reversed on fan relay. 5 is normally closed and 6 is normally open. drawn 6 is normally open and 5 is normally closed.
Attached Images
File Type: jpg RHEEM.JPG (30.3 KB, 2 views)

Last edited by HayZee518; 08-26-2009 at 12:04 PM..
Reply With Quote
  #10 (permalink)  
Old 08-26-2009, 07:52 PM
New Member
 
Join Date: Aug 2009
Posts: 8
Thanks: 2
Thanked 0 Times in 0 Posts
herbertjd13 is on a distinguished road
Not sure what to do next.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,946
Threads: 7,778
Posts: 33,327
Top Poster: HayZee518 (4,978)
Welcome to our newest member, mitchell123
» Online Users: 20
0 members and 20 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 06:07 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0