I have a 1989 carrier furnace with problems
model 58sx080-gg-1, I have problems with pilot assemblies before, this problem is probably a a pilot assembly, when I switch the furnace to heat, I don't now here the gas valve, kick in I have switched it on a nd off a few times then I hear the gas valve kick in I looked at the pilt kick in, but it doesn't light the burner and the blower doesn't kick in , checked the board that and the blower do work, what could it be thanks chen
|

10-03-2009, 10:08 PM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
|
|
|
the heater goes through a series of self checks before it starts. before the gas turns on the unit goes through a purge cycle. once this is done the gas valve for the pilot opens and the hot surface igniter attempts to fire up the pilot. if there is a flame a flame rod or cd cell verifies that there is a flame before the main gas valve opens. some factors come into play here. if your unit has a forced exhaust fan this may need to be operating and an air sail switch must make up before the main valve opens. no flame the unit goes into lockout. no exhaust air the unit goes into lockout. tell us what you have.
|
|
The Following User Says Thank You to HayZee518 For This Useful Post:
|
|

10-05-2009, 01:54 PM
|
|
New Member
|
|
Join Date: Oct 2009
Posts: 5
Thanks: 4
Thanked 0 Times in 0 Posts
|
|
|
my 1989 furnace
where on the internet can I download a manual for repairing or troubleshooting this furnace, this what my seems to do, the fan is auto, when I turn the thermostat to heat usually I could here a clunk thats is probably the gas valve opening for the pilot, I had done this a few times 1 of 3 I would here this, no heat, so went down to furnace, took off doors looked in at the pilot, pushed the interlock in, same thing 1out of 3, I would get the clunk, when the clunk was hear I would get a pilot and further clicking, waiting more than 5 minutes, it wouldn't lit the burners and turn the blower on, I have had problems before with the pilot assembly, I was told that dampness from humidity in the summer was causing this, I haven't had problems for 2 years since I tape the pipes outside shutoff, but again I have problems what do you recommend thanks
|

10-05-2009, 03:28 PM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
|
|
|
for a furnace that old 20 plus years I'd doubt you'd find any electrical diagram. dampness will play into the flame detect circuit just as if it were shorted to ground. is yours a standing pilot?
|

10-05-2009, 09:16 PM
|
|
 |
Handyman
|
|
Join Date: Apr 2006
Location: Ohio
Posts: 81
Thanks: 0
Thanked 6 Times in 6 Posts
|
|
|
Last edited by hvacwiz; 10-05-2009 at 09:18 PM..
|
|
The Following User Says Thank You to hvacwiz For This Useful Post:
|
|

10-06-2009, 12:44 PM
|
|
New Member
|
|
Join Date: Oct 2009
Posts: 5
Thanks: 4
Thanked 0 Times in 0 Posts
|
|
|
1989 carrier
this furnace does have a pilot assembly, it does still click and do get a pilot but not getting it to lit the burners and bring in the blower, so it must be something in the electronics of the pilot assembly correct thanks
|

10-06-2009, 03:50 PM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
|
|
|
if there is a lit standing pilot then I would have to suspect the flame detector is also working. the flame detect generates a very small dc voltage that keeps the pilot valve open. my next area would be the wall thermostat not working or the transformer feeding the whole circuit.
|

10-06-2009, 06:46 PM
|
|
 |
Handyman
|
|
Join Date: Apr 2006
Location: Ohio
Posts: 81
Thanks: 0
Thanked 6 Times in 6 Posts
|
|
|
The 3wire pilot has a set of contacts in it, when the pilot heats up enough it switches over to anthor set of contacts, these contacts send 24v to your gas valve. Like i said if you change the pilot burner your problem should be solved. this is the most common replaced part on this furnace.
|
|
The Following User Says Thank You to hvacwiz For This Useful Post:
|
|

10-06-2009, 06:49 PM
|
|
 |
Handyman
|
|
Join Date: Apr 2006
Location: Ohio
Posts: 81
Thanks: 0
Thanked 6 Times in 6 Posts
|
|
Quote:
Originally Posted by HayZee518
if there is a lit standing pilot then I would have to suspect the flame detector is also working. the flame detect generates a very small dc voltage that keeps the pilot valve open. my next area would be the wall thermostat not working or the transformer feeding the whole circuit.
|
If the t-stat wasnt working he would not have a pilot at all. this furnace only lites the pilot on a call for heat.
|
|
The Following User Says Thank You to hvacwiz For This Useful Post:
|
|

10-07-2009, 07:50 PM
|
|
New Member
|
|
Join Date: Oct 2009
Posts: 5
Thanks: 4
Thanked 0 Times in 0 Posts
|
|
|
1989 furnace
thanks a lot guys it was my pilot assembly, I bought one never installed one before but it did everything as advertising, not that cold yet but took the chill out, I will refer back again for sure in spring my condensing unit outside just before it got cooler was making a noise and made the lights blink inside the house, it has to be either the compressor or the condensing fan motor, hoping it's just the fan thanks again 
|
 |
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 12,943
Threads: 7,776
Posts: 33,324
Top Poster: HayZee518 (4,977)
|
| Welcome to our newest member, GLE3 |
» Links |
|
» Sponsors |
|
|
|