    furnace is going off on high limit

    My unicell furnace is overheating. This causes it to shut down. The repairman says "The furnace is going off on high limit. The heat exchanger is getting cherry red and is a fire hazard. The vent and combustion air are too small for the size of the furnace. The furnace is too big for the duct work and should be replaced."
    He said its a 120 btu and my house should only need a 75 btu.

    The furnace is 11 years old. Do I really need a new one? Can't something else be done? I have had the igniter changed, but that only solved the problem for about 3 weeks.

  2. #2
    Join Date
    Nov 2003
    Location
    .
    Posts
    453
    Thanks
    0
    Thanked 1 Time in 1 Post
    Before I give you any advice on this problem, one thing puzzles me; "you say the unit is 11 years old, and the duct, etc is too small." When did this "overheating on limit" start to occur. If it was because of the unit being too big and the ducts too small this would have happened right from the start 11 years ago..... An oversised furnace will have a "short cycle" effect, and will cause the unit to cycle for short, but oftener times.... (its best to have a unit the proper size, but slightly under is better than over.... Normally "limiting out" on a proper sized unit is caused by dirty filters, improper air speed, obstructions in the air flow, dampers closed,etc. Again I ask ,when did this first occur.? Post back with this info and we will try to advise you further.Thanks. Hube

  3. #3
    Join Date
    Feb 2004
    Location
    Elmira, NY.
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    This happened a couple of years ago for the first time, and bigger cold air return ducting was installed. It has run fine since, until last month. The high limit switch would shut down, but I could get it running again by shutting the thermostat down to 50 then turning it back on. A repairman installed a new igniter, and changed piping outside to eliminate drafts. This worked until last night. Now it won't work at all. Even shutting the power switch off has no effect.Also forgot to mention.. I pulled out a filter that I hadn't changed in a while and it fell apart inside while the furnace was running. I told repairmen this.

  4. #4
    Join Date
    Nov 2003
    Location
    .
    Posts
    453
    Thanks
    0
    Thanked 1 Time in 1 Post
    The best thing to do right NOW would be to get that Damaged old Filter out of there. It is probably obstructing the AIR FLOW and this is what is causing the Limit to kick off the unit.Also, it seems like this furnace needs some TLC (maintenance work) such as cleaning the fan impeller blades, duct work vacuuming,etc. Let us know how you make out. Hube

  5. #5
    Join Date
    Feb 2004
    Location
    Elmira, NY.
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    After being off all night, I turned the thermostat up to try it, and it is now working again. Thanks for your help. I will get someone in to do the maintenance work.

  6. #6
    Join Date
    Feb 2004
    Location
    .
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    i have seen this same thing before if the unit is to big it can cause this to happen short cycle is the same as going off on limit you can have a tech shut off one of the burners and and cap off a cell but you need to check out the footage of the house to a btu chart to see if you are over sized

  7. #7
    Join Date
    Feb 2004
    Location
    .
    Posts
    8
    Thanks
    0
    Thanked 0 Times in 0 Posts
    quote:Originally posted by msdalem1

    This happened a couple of years ago for the first time, and bigger cold air return ducting was installed. It has run fine since, until last month. The high limit switch would shut down, but I could get it running again by shutting the thermostat down to 50 then turning it back on. A repairman installed a new igniter, and changed piping outside to eliminate drafts. This worked until last night. Now it won't work at all. Even shutting the power switch off has no effect.Also forgot to mention.. I pulled out a filter that I hadn't changed in a while and it fell apart inside while the furnace was running. I told repairmen this.
    The evaporator coil can plug with dirt and block the air flow and overheating occures.

  8. #8
    Join Date
    Feb 2004
    Location
    .
    Posts
    8
    Thanks
    0
    Thanked 0 Times in 0 Posts
    quote:Originally posted by bbgru1

    i have seen this same thing before if the unit is to big it can cause this to happen short cycle is the same as going off on limit you can have a tech shut off one of the burners and and cap off a cell but you need to check out the footage of the house to a btu chart to see if you are over sized
    If you block a burner on a 80% furnace, the flue may condense water back into the furnace due to the lowered flue temperature.

  9. #9
    Join Date
    Dec 2012
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Hube View Post
    Before I give you any advice on this problem, one thing puzzles me; "you say the unit is 11 years old, and the duct, etc is too small." When did this "overheating on limit" start to occur. If it was because of the unit being too big and the ducts too small this would have happened right from the start 11 years ago..... An oversised furnace will have a "short cycle" effect, and will cause the unit to cycle for short, but oftener times.... (its best to have a unit the proper size, but slightly under is better than over.... Normally "limiting out" on a proper sized unit is caused by dirty filters, improper air speed, obstructions in the air flow, dampers closed,etc. Again I ask ,when did this first occur.? Post back with this info and we will try to advise you further.Thanks. Hube
    I have a 7 yr old 100 BTU mid efficency furnace that is be having in a similar manner (sensor shuts burner off when temperature is approx 160 degrees, then when it cools the burner starts up). I believe this has been occurring since the furnace was installed. I assumed this was normal, but recently Direct Energy checked the furnace for a maintenance and strongly suggest that I replace the unit with a 60 BTU because this one is too big for my modest house (1800 sq ft). Direct EA replacement will cost approx $5,500 for a high efficiency 60 BTU unit. ....So I'm searching for a second opinion .....
    and question Why would a private company install a unit that is too big causing safety issues and causing the heat sensor to trip too often? ...G Wile

  10. #10
    Join Date
    Jul 2004
    Location
    Saint Regis Falls, NY, USA.
    Posts
    8,287
    Thanks
    1
    Thanked 455 Times in 443 Posts

    furnace

    perhaps the after thought was in place when the house was designed. that is, expansion of the property and there being no need to increase the size of the dwelling furnace. now its causing problems. look into the circulator fan see if there are provisions to slow down the speed. with max speed/airflow, undersized ducting will cause a back pressure to the system which may kick the unit off on a high pressure limit or high current on the motor.