    HELP..Goodman GMP 100-4, no blower in "auto"

    *With the stat in "heat" mode & fan in "auto", furnace cycles normally until the burner lights, burns for 30 sec... No blower & shuts down. Recycles, ignitor glows but no ignition. Cleaned flame sensor, no difference.

    *With stat in "heat" & fan in "on" position, everything works fine, heater runs, shuts off at set temp. (Manually turn off fan.) The flame sensor must be working with this method if burner stays lit, right?

    What function is bypassed with fan in "on" that is not working with fan in "auto"?

  2. #2
    paul52446m is offline Journeyman
    Join Date
    Nov 2009
    Location
    Houghton Lake Mi.
    Posts
    690
    Thanks
    2
    Thanked 95 Times in 94 Posts
    Quote Originally Posted by TLL View Post
    *With the stat in "heat" mode & fan in "auto", furnace cycles normally until the burner lights, burns for 30 sec... No blower & shuts down. Recycles, ignitor glows but no ignition. Cleaned flame sensor, no difference.

    *With stat in "heat" & fan in "on" position, everything works fine, heater runs, shuts off at set temp. (Manually turn off fan.) The flame sensor must be working with this method if burner stays lit, right?

    What function is bypassed with fan in "on" that is not working with fan in "auto"?
    haven't really heard of that one. `If it did not prove on the first try, that would be ether the flame rod or the electronic board. If you get no flame on the second try but you get glow bar. i would say it has to be a problem in your electronic board. I don't know if it run long enough for the blower to come on on the first try. Ether way i think its in the board. Later Paul
    Last edited by paul52446m; 10-30-2010 at 10:27 PM.

  3. #3
    TLL
    TLL is offline New Member
    Join Date
    Oct 2010
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by paul52446m View Post
    haven't really heard of that one. `If it did not prove on the first try, that would be ether the flame rod or the electronic board. If you get no flame on the second try but you get glow bar. i would say it has to be a problem in your electronic board. I don't know if it run long enough for the blower to come on on the first try. Ether way i think its in the board. Later Paul
    Thanks Paul. Being unemployed, I was really hoping it would be something simple and cheap, but I fear you are right.