Washer "Tap-n'-Drain" Trap?
Does a washer "tap-n'-drain" get trapped[?] I assume it does but our half-as[:0]ed contractor didn't do it. Should it be[?] Our current one is trapped, but the new one currently is it. I need to know before drywall goes up...[V]
Thanks
~Jonathon Reinhart
|

07-21-2004, 07:46 AM
|
 |
Deity
|
|
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,201
|
|
|
By tap-n-drain i presume you mean the recessed type "washer Box" that has both the water supply valves and drain line in a common recessed box. All drains require a trap. In the case of the recessed box the trap is normally installed under the floor (basement or crawl space) with a riser going up to the box.
If the drain is over a concrete slab such as in a basement or one story on slab construction the drain most likely has a trap under the concrete. If it does not have an under slab trap, or in situations where you can not access it under floor the option is to install a trap in the wall, then install a service access panel.
|

07-21-2004, 09:28 AM
|
|
Apprentice
|
|
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
|
|
|
Here code would call for a trap on it . There in the wall just above the floor so it could be worked on if need be.
ED[:0]
My mistakes dont define me they inform me.
|

07-21-2004, 06:08 PM
|
 |
Handyman
|
|
Join Date: Jul 2004
Location: OH, USA.
Posts: 109
|
|
|
Thanks, they said "oh, we never put in a trap for the washer!"... Anyway, we asked them to, and they will. In the crawlspace...
Thanks again
~Jonathon Reinhart
|

07-28-2004, 08:56 PM
|
 |
Deity
|
|
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,201
|
|
|
For the record i need to correct a previous post. A laundry service drain trap may not be installed under the slab. If a laundry is over a slab floor the trap must be greater than 6 inches but not more than 18 inches above the floor. If it is installed in the wall a suitable access panel at least 12 x 12 inches must be provided for service. Now in regards to traps. With the singular exception of the water heater T&P discharge line, all drain connections must have a trap. The T&P (temperature and pressure relief valve) discharge line must undiminished in size and must be connected by means of an indirect waste or a line must be run outside the structure and dischage downward with the opening not less than 6 nches above average grade, and there may be no valves on the line, and no threads on the discharge end of the line.
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
 |
» Forum Navigation |
|
|
» Links |
|
|
All times are GMT -5. The time now is 08:37 AM.