Washer "Tap-n'-Drain" Trap?

Does a washer "tap-n'-drain" get trapped[?] I assume it does but our half-as[:0]ed contractor didn't do it. Should it be[?] Our current one is trapped, but the new one currently is it. I need to know before drywall goes up...[V]

Thanks

~Jonathon Reinhart
Reply With Quote
  #2 (permalink)  
Old 07-21-2004, 08:46 AM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,211
LazyPup is on a distinguished road
By tap-n-drain i presume you mean the recessed type "washer Box" that has both the water supply valves and drain line in a common recessed box. All drains require a trap. In the case of the recessed box the trap is normally installed under the floor (basement or crawl space) with a riser going up to the box.
If the drain is over a concrete slab such as in a basement or one story on slab construction the drain most likely has a trap under the concrete. If it does not have an under slab trap, or in situations where you can not access it under floor the option is to install a trap in the wall, then install a service access panel.
Reply With Quote
  #3 (permalink)  
Old 07-21-2004, 10:28 AM
Apprentice
 
Join Date: Apr 2004
Location: FL, USA.
Posts: 330
imeduc
Here code would call for a trap on it . There in the wall just above the floor so it could be worked on if need be.

ED[:0]

My mistakes dont define me they inform me.
Reply With Quote
  #4 (permalink)  
Old 07-21-2004, 07:08 PM
Kidd6488's Avatar
Handyman
 
Join Date: Jul 2004
Location: OH, USA.
Posts: 109
Kidd6488 is an unknown quantity at this point
Send a message via AIM to Kidd6488
Thanks, they said "oh, we never put in a trap for the washer!"... Anyway, we asked them to, and they will. In the crawlspace...

Thanks again

~Jonathon Reinhart
Reply With Quote
  #5 (permalink)  
Old 07-28-2004, 09:56 PM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,211
LazyPup is on a distinguished road
For the record i need to correct a previous post. A laundry service drain trap may not be installed under the slab. If a laundry is over a slab floor the trap must be greater than 6 inches but not more than 18 inches above the floor. If it is installed in the wall a suitable access panel at least 12 x 12 inches must be provided for service. Now in regards to traps. With the singular exception of the water heater T&P discharge line, all drain connections must have a trap. The T&P (temperature and pressure relief valve) discharge line must undiminished in size and must be connected by means of an indirect waste or a line must be run outside the structure and dischage downward with the opening not less than 6 nches above average grade, and there may be no valves on the line, and no threads on the discharge end of the line.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,163
Threads: 6,802
Posts: 28,117
Top Poster: HayZee518 (3,845)
Welcome to our newest member, Foley
» Links

» Online Users: 51
3 members and 48 guests
Hube, pat elmore, thedcdude
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 10:34 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0