To get a rough estimation of where your main drain line runs go outside and look on the roof. Your main drain is either a 3 or 4 inch line and it must run undiminished in size up to the main vent. You should see it protruding out of the roof in a near proximity to one of the bathrooms and toward the opposite end of the house from the septic tank. All of the toilets may be connected on the main line, but most likely at least one is on a lateral line. If you have a lateral line it will most likely also have a vent but it may not, depending on the length of the lateral from the main drain line. You may also see another vent in the vincinity of the kitchen or laundry,but again, that would be determined by the lengh of the trap inlets from the main drain. If all three toilets are effected the stoppage will either be on the upstream end toward the vent, past the last toilet which is restricting the venting action, or the obstruction would have to be downstream (toward the septic tank) from the first toilet, otherwise all three would not be effected. There is a cleanout at the base of your wet vent riser, which is on the upstream end of the run. To clean the main drain they should rod it out (snake the drain) from the base of the stack, then pull the toilets on the lateral lines and rod out through the toilet flange. (Toilets are considered approved cleanouts because when a toilet is lifted you have an unobstructed run). As far as the toilets being old, that is a bunch of baloney. A toilet is simply a bowl of water with a built in trap. There are components in the water fill and flushing mechanism in the tank that require periodic maintenance but short of cracking or breaking the bowl, or dropping something into it that gets caugth in the trap, the bowls are foolproof. The only thing that goes wrong with bowls is a failure of the wax rings that seal the bowl to the closet flange.
|