The codes are very specfic on thins matter. The pipe must run under the slab and the depth of burial at the footer wall MUST BE frost depth +6in. Begin by establishing a line from the point were you intend to to install the toilet and running as straight as possible to the septic tank inlet line connection. Measure the distance from the footer wall penetration point to the septic tank connection point and compute a pitch drop of 1/8in /ft. Add the required pitch and the frost burial depth and that will indicate the required finish grade elevation minimum for the slab.
Example: using 50 ft for the footer wall penetration to septic tank inlet distance an a 12in frost line.
1/8in = .0125 inches
required pitch 50 x .0125 = 6.25in drop
frost + 6 inches = 18inches
minimum depth = frost depth + req. pitch= 18in + 6.25in = 24.25in.
MINIMUM SLAB FINISHED ELEVATION 24.25in above the septic tank inlet line.
From the point of wall penetration to the water closet (toilet) the line must be pitched at 1/8in/ft rise to water closet but must be a minimum of 12 inches below the water closet flange to permit a 90 sanitary quater bend (90 deg elbow up to closet flange)
The minimum diameter of line is 3inches for the line under the slab, to the location of the toilet and running undiminished in size up and out through the roof as a main vent.
Additional required fittings:
Line must be sleeved when it penetrates the footer wall. Sleeve is a length of pipe at least two trade sizes larger than the desired pipe and long enough to reach through the footer wall and extend 3 inches on either side. The space between the inside of the sleeve and outside of the desired pipe must be filled with expansion foam.
At a point 3 ft outside the footer wall a two way cleanout must be installed. (Additional cleanouts are required for each additional 80 ft of run. or at any point where the line makes a 90 deg change in direction)
Must be a cleanout at the base of the vent stack.
Vent must be connected to the building drain on the downstream side of the water closet(toilet) waste arm.
PROHIBITED FITTINGS:
A sanitary tee may not be installed on its back. To make the connection from the building drain to the vent stack you must use a Sanitary wye and 1/8 bend or a sanitary combo.
email me if you would like a drawing with these specs an specific code references.