JOINING DISSIMILAR PIPE ILLUSTRATED

Reply With Quote
  #2 (permalink)  
Old 12-19-2004, 11:39 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
Thanks: 0
Thanked 0 Times in 0 Posts
kactuskid is on a distinguished road
Really nice drawings LazyPup. I have a guestion, is it ok to use a brass fitting to connect galvinized piping to copper instead of a dieletric union? I see this alot and figured it to be a good substitute to ensure against electrolisis.
Reply With Quote
  #3 (permalink)  
Old 12-19-2004, 02:26 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
Zinc-Copper, Zinc-Brass is electrolytically active. The dielectric union eliminates the "battery" across the joint.
Reply With Quote
  #4 (permalink)  
Old 12-25-2004, 08:34 PM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
LazyPup has a spectacular aura about
The code prohibits directly coupling copper to iron, but in addition to dielectric nipples and dielectric unions, it does permit the use of a 6 inch hardened bronze nipple.

In some jurisdictions the inspectors will permit valve bodies to be used as the transition fitting if the valve has a hardened bronze body but technically they would not pass for two reasons. 1. They lack the code minimum 6" length, and 2. there is no way to insure that the valve will be replaced with a hardened bronze body valve during future maintenance.
Reply With Quote
  #5 (permalink)  
Old 02-14-2006, 05:17 PM
New Member
 
Join Date: Feb 2006
Posts: 9
Thanks: 0
Thanked 0 Times in 0 Posts
WD8CDH is an unknown quantity at this point
Hi LazyPub,

How about those "dielectric nipples" that are just a galvanized nipple with a plastic lining? I can't see how they would work.

Ron
Reply With Quote
  #6 (permalink)  
Old 07-19-2006, 07:41 AM
New Member
 
Join Date: Jul 2006
Posts: 10
Thanks: 0
Thanked 0 Times in 0 Posts
Sauna is an unknown quantity at this point
Very useful indeed. Thanks for the drawings.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote
  #7 (permalink)  
Old 08-24-2008, 11:33 PM
New Member
 
Join Date: Oct 2005
Location: .
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
JimV is an unknown quantity at this point
Galvanized to Bronze Valve

It seems to be pretty standard to use bronze valves with threaded galvanized pipe. Why doesn't that cause problems, since they are dissimilar? Also, I have been told that having copper and galvanized in direct contact will not only cause the galvanized to corrode at the point of contact, but will also cause problems downstream. Any thoughts?
Reply With Quote
  #8 (permalink)  
Old 08-25-2008, 05:39 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 4,977
Thanks: 0
Thanked 102 Times in 102 Posts
HayZee518 will become famous soon enough
Send a message via Yahoo to HayZee518
just for ha-ha's take a look at the periodic table of elements from chemistry class back from high school. one side is active gasses other side is active metals. here you'll find Cu=copper, Zn=zinc, Fe=iron, Pb=lead, Tin=Sn. Bronze and brass are alloys of two metals. Brass is copper and tin, bronze is copper and nickel. so, if you mix any of the active metals you can create corrosion between the joints unless you use an alloy.
Reply With Quote
  #9 (permalink)  
Old 08-25-2008, 02:58 PM
New Member
 
Join Date: Aug 2008
Posts: 10
Thanks: 0
Thanked 0 Times in 0 Posts
jackmcmanus21 is an unknown quantity at this point
very useful drawings, thank you!
__________________
[SIZE=2]
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
[/SIZE]
Reply With Quote
  #10 (permalink)  
Old 08-30-2008, 11:11 PM
New Member
 
Join Date: Aug 2008
Posts: 1
Thanks: 0
Thanked 0 Times in 0 Posts
jackiensteve is an unknown quantity at this point
Thanks for the info! I have a question that no one in any of the big boxes can answer. We jackhammered the basement floor to remove an old cast iron bowl drain and to install a shower. The existing pipe into the floor drain is 2.5 inch cast iron. We need 2" pipe for the shower. WE have searched high and low for a male threaded reducer and can't find anything 2.5". whatever we use must also be able to have concrete poured on top of it. Would the illustration on joining cast iron and pvc work in lieu of not being able to find ANY 2.5" threaded pipes?
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,943
Threads: 7,776
Posts: 33,324
Top Poster: HayZee518 (4,977)
Welcome to our newest member, GLE3
» Online Users: 48
2 members and 46 guests
GLE3, paul52446m
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 07:44 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0