Water Heater TPR valve
I have vented my TPR valve outside using Schedule 40 PVC. Home inspector says no good. [u]Fittings not rated for 210 degress and 150 PSI. What is recommended for use and must it be rated the same as the valve? Can I use CPVC even thought its rated at 180 degrees and 100 PSI? After all, it vents outside with nothing to hold the pressure. All help appreciated.
|

11-30-2005, 09:29 PM
|
|
 |
Deity
|
|
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
|
|
|
You inspector is correct. PVC pipe may be used for "SUPPLY PIPING" (water line from the source to the structure) but MAY NOT be used for any "Distribution piping" (water piping within the structure.)
There are a number of code important code points in regards to water heater T&P relief valves:
Temperature and Pressure Relief Valve drain piping per the International Residential Code (IRC) and the Uniform Plumbing Code(UPC).
REF: IRC 2803.6.1 & UPC-608.5
1. The T&P drain must terminate outside the structure, or inside the structure into an approved indirect waste receptor. (In an unfinished basement that has a floor drain the T&P may terminate on the floor.
2. The IRC requires the point of discharge to be within 6" of the receptor or finished grade when outside.
3. The UPC requires the point of discharge to be within 6" to 24" above the receptor or finished grade when discharged outside.
4. The drain line diameter MUST BE equal to or greater than the T&P dischrge port outlet.
5.The drain line Must be pitched in the direction of the discharge port. May not run uphill, may not be trapped and may not have any restrictions to flow.
6.There may be no kinks or restrictions to flow.
7. The discharge end of the pipe MUST BE visible.
8.There shall be no shutoff valves and the discharge end of the pipe may not be threaded.
9. Must be plumbed with the same materials as approved for "Water Distribution" I.E. Galvanized Iron pipe, Hard drawn Copper Pipe or CPVC (Local codes may not permit CPVC)
10 TPRV may not discharge into the water heater drip pan.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 12,944
Threads: 7,777
Posts: 33,327
Top Poster: HayZee518 (4,977)
|
| Welcome to our newest member, Peabarter |
» Links |
|
» Sponsors |
|
|
|
All times are GMT -5. The time now is 11:19 PM.