heat upstairs none downstairs
dear board,
I have a 2 zone heating system and one zone is working but the other is not. I have a gas weil mclain and was wondering if i need to bleed and if so how would I do that. I changed the battery in the thermostat to no avail. any help would be useful as i am stymied. mike
|

01-20-2006, 03:08 PM
|
|
 |
Deity
|
|
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,258
Thanks: 0
Thanked 14 Times in 14 Posts
|
|
|
While there are a number of different methods that can be used to create zones primarily in a residential application a separate main line is run to each zone. We can then either install a separate circulator pump on each zone line or the system may have one circulator pump and separate control valves on each line.
A thermostat is then installed in each zone and the thermostat would either open and close the zone valve or it may control the circulator pump for that zone.
You stated that you have heat in one zone so if your system has a single circultor pump we can assume for the moment that the pump is working okay.
The problem will most likely be confined to the Thermostat, thermostat control cable or the zone valve controling that zone.
|

01-20-2006, 03:31 PM
|
|
New Member
|
|
Join Date: Jan 2006
Location: newton, nj, USA.
Posts: 7
Thanks: 0
Thanked 0 Times in 0 Posts
|
|
|
thannks for your response
i have been doing a little tinkering. there is only one circulater. pump seems fine. therre are 2 pipes that go out from the furnace and before the man cut off handle there are 2 silver boxes. the one line is barely warm. there is a manual setting underneath the box and i turned it from automatic to manual. this allowed that pipe to get hot. the pipe on the return remained cold. now if i left the backflow (or at least that is what I think it is) in manual and therre were possibly a frozen pipe would it eventually unfreeze the pipe or would the pressure from the water not going anywhere burst the pipe.
|

01-20-2006, 03:49 PM
|
|
New Member
|
|
Join Date: Jan 2006
Location: newton, nj, USA.
Posts: 7
Thanks: 0
Thanked 0 Times in 0 Posts
|
|
Quote:
quote:Originally posted by LazyPup
While there are a number of different methods that can be used to create zones primarily in a residential application a separate main line is run to each zone. We can then either install a separate circulator pump on each zone line or the system may have one circulator pump and separate control valves on each line.
A thermostat is then installed in each zone and the thermostat would either open and close the zone valve or it may control the circulator pump for that zone.
You stated that you have heat in one zone so if your system has a single circultor pump we can assume for the moment that the pump is working okay.
The problem will most likely be confined to the Thermostat, thermostat control cable or the zone valve controling that zone.
|
I fooled around with the backflow and put it on manual and the pipe heated up. the pipe on the return did not heat up however. should I just keep the backflow box on manual, open until i figure it out or should I not. i don't know. what do you think.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 12,950
Threads: 7,780
Posts: 33,338
Top Poster: HayZee518 (4,981)
|
| Welcome to our newest member, morris12 |
» Online Users: 50 |
| 0 members and 50 guests |
| No Members online |
| Most users ever online was 400, 06-22-2009 at 07:11 AM. |
» Links |
|
» Sponsors |
|
|
|
All times are GMT -5. The time now is 04:32 PM.